Generator Louvers

07/04/2007 12:35 AM

I have a project that requires our building louvers to open when one of the generators starts to run. There are 4 actuators per generator rating 120Vac 0.9 A. We have 5 generators, 3 are what we call parallel generators feeding a common bus. The other two fed their own separate bus. I was told to have this connected to a run relay located in the master control switchgear of the parrallel generator. Is this possible? Does anyone have a similar situation to this? If so, do you have a schematic diagrams showing these connections.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Generator Louvers

07/05/2007 8:13 AM

E-Z...Why the switchgear? Read on!!! Why not have the louver 120v control circuit connected to parrallel switching relays (1) on each of the (5) gen/sets with form "C," N.O. contacts (dry, no power switching duty only) from each of the generators. As soon as any one of the gen/sets starts the contacts will close and the louvers will open. Use utlility heavy duty relays with 10 amp contacts for long life. I'm sure the relays can be ordered or furnished by the gen/set manufacturer.

I subscribe to K.I.S.S. process.

Economy of design is! Easy does as easy goes.

Register to Reply
Anonymous Poster
#3
In reply to #1

Re: Generator Louvers

07/05/2007 9:10 AM

The Kiss rule is GREAT.

Remember that it cost money to run equipment.

Install a thermostat with the control circuit.You

only need the fans running to remove heat.Why pay extra to move good air.

AS a Canadian who used many generators we try to save money.Yes and in the COLD winter

we sent rad. heat to bldg to get free waste heat.

A canadian KISS supporter.

Register to Reply
Active Contributor

Join Date: May 2007
Posts: 15
#4
In reply to #3

Re: Generator Louvers

07/05/2007 10:29 AM

KISS is good, we pratice it at all times, so I guess we should ask ROMY what these louvers are for? Cooling air? Combustion air? Or both

Register to Reply
Active Contributor

Join Date: May 2007
Posts: 15
#2

Re: Generator Louvers

07/05/2007 8:53 AM

The louvers should be designed to allow for the air requirements for each Gen. set typical, the start contacts close, the damper motors drive the dampers open, the end switch on the damper motor closes when the dampers are fully open and starts the Gen. set. Be careful starting the Gen set befroe the dampers are open, you could collapse the dampers if the Gen, set has a large air requirement, combustion air and cooling air. You can have any Gen. set open all dampers or just the damper for that Gen. set. A simple control circuit.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5

Re: Generator Louvers

07/05/2007 10:48 AM

If master control panel has a power on run light on it a circuit can be connected in parallel to a control relay for the buildings louvers. When generators turn on power supplied to the run light will also be applied to the coil of the relay which will open the louvers. Current draw from a small relay should not cause any problems.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#6

Re: Generator Louvers

07/05/2007 10:49 AM

You could install relays that would be energized when the diesel start switch is turned to the "on" position. We had 24 volt motors that drove the louvers on IHI container cranes and would open at the first starter switch position.

__________________
Eschew obfuscation.
Register to Reply