Min Clearance From Transformer To Building

10/29/2014 11:20 PM

Whats the minimum clearance required from transformer oil containment to building window or door without fire wall. Its 240 kv 400 MVA transformer with more than 5000 gallon oil. I checked IEEE 979 and found it should be 15.2m. But if I have oil containment still I have maintain this distance or i could keep 10.7m as per section 7.2.6. I checked NEC and its says same thing. FOR CEC which standard I could follow. How this distance shall be meausured- from edge of oil containment to edge of building wall or from edge of transformer. I would appreciate if anyone give me idea.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Min clearance from transformer to building

10/29/2014 11:45 PM

Consult IS 2026 and the local building codes which may be more stringent than the IS.

Are you sure you only want 10.7m between your building and this:

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 13
#2
In reply to #1

Re: Min clearance from transformer to building

10/29/2014 11:54 PM

Thanks for your reply. I found this in IEEE 979 where mentioned "where containment is provided in accordence with 8.1, other types of sub equipment should be no closer than 10.7m to n adjacent piece of mineral oil insulated equipments anticipated flame front or containment boundary"

Register to Reply
Power-User

Join Date: Oct 2009
Posts: 176
Good Answers: 4
#9
In reply to #1

Re: Min clearance from transformer to building

10/31/2014 10:32 AM

Only 10.7m between his building and a busted jpeg? The horror!
Please re-post, or put up a link. I would really like to see what this was.

Register to Reply
Power-User

Join Date: Oct 2009
Posts: 176
Good Answers: 4
#11
In reply to #1

Re: Min clearance from transformer to building

11/17/2014 11:08 AM

And there it is. Yikes.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Min Clearance From Transformer To Building

10/30/2014 9:45 AM

What do you mean by the term "containment"? Catching the oil if there is a leak or preventing the oil from hitting a structure should the transformer go boom?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Min Clearance From Transformer To Building

10/31/2014 12:03 AM

Having looked at the OP's previous posts I think he would be better employed well away from anything involving power.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#8
In reply to #4

Re: Min Clearance From Transformer To Building

10/31/2014 9:32 AM

I suspected that such was the case from the wording of the OP's post.

I would have checked other threads he started to confirm, but it sounds like you did the legwork for me.

Often times when I see a post like this, the poster is from/working in a region that has NO electrical or fire codes whatsoever. (A place that could be said is trying to develop itself into a Developing Nation.) Other times it's people who say 'The rules say I need a 6" reinforced concrete slap to support this, can I use scrap pieces of 1/4 inch chipboard?" In the first case, it's understandable: They have no clue and come to us for advice. Their problem is that they expect us to give Professional Opinions on how do to it, and nobody wants to deal with the liabilities of 'over-the-phone, no-eyes-on-project' engineering.

The second group concerns me, how did they so long with the part of their brain that tells them when something is a bad idea is turned off? Shouldn't they have earned themselves a Darwin Award BEFORE they ended up in a position where they could potentially cause so much death and destruction?

(self-marking as OT due to the rant-like nature of the post.)

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#5

Re: Min Clearance From Transformer To Building

10/31/2014 3:35 AM

From the evidence I saw the ensuing oil fire was so great light fittings on the exterior of a building were melted at over 20m away and the surrounding concrete apron was pockmarked where the burning boiling oil had landed.

This transformer was smaller than the one you are proposing but was at the end of a similar fault level.

Your building wants to be nowhere near a transformer like this. I assume we are talking blast protected building and not a portacabin ........

Also to consider is the EMF generated by the transformer which we are all told is safe.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#6

Re: Min Clearance From Transformer To Building

10/31/2014 7:12 AM

It is measured from the oil containment pit. and I think you will still require a fire wall. It depends where you are and what your client requires for the site and also the fire regulations if you are in the USA. Check with your local fire dept as well as they will be involved somewhere along the line.. The space required is for fire fighting as well as preventing the spread of the fire to adjacent areas and buildings.

The standards are only guidelines of minimum requirements, not set distances and dependent on the area and catchment systems being used. Bunded to the Tfx only or drained to a catchment tank vie pipe works.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Min Clearance From Transformer To Building

10/31/2014 7:40 AM

Correct IQ! However, sahababu71, see also NFPA 850 Recommended Practice for

Fire Protection for Electric Generating Plants and High Voltage Direct Current Converter Stations

ch.5.2.4 Outdoor Oil-Insulated Transformers.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Min Clearance From Transformer To Building

11/08/2014 3:08 AM

I have not the last edition of IEEE 979.However in IEEE 979-2004 ch. 4.4 Transformer outdoor installations NFPA 850 is recommended.

NFPA 850 -2005 requires 50 ft Minimum (Line-of-Sight) Separation Without Firewall.

With a firewall you may reduce the distance.

__________________
Julius
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers: