Short Circuit Current Capacity of Transformers Bushings During a Fault

12/17/2014 2:06 PM

Dear all,

The requirement for HV system fault level is 63kA for 1 seconds and the short circuit current capacity of my transformer bushing is 20kA for 2 seconds.Is there a way to convince the customer that I don't need to select the bushings of the transformer at least with same short circuit current capacity as system fault level ? Or should I select the bushings at least with 63kA / 1 sec for short circuit capability ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: SHORT CIRCUIT CURRENT CAPACITY OF TRANSFORMER BUSHINGS DURING A FAULT

12/17/2014 2:11 PM

Go with your bushings.
They'll be more colorful.

Register to Reply Good Answer (Score 3)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: SHORT CIRCUIT CURRENT CAPACITY OF TRANSFORMER BUSHINGS DURING A FAULT

12/17/2014 2:45 PM

Get them to change the requirement, however if it is a requirement rather than just an over-rating then offer the right bushings or get proof the bushings you want to supply will actually meet the customer's requirements.

A call through to the bushing supplier may quickly clear things up.

__________________
jack of all trades
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/17/2014 4:01 PM

Do you really think that a 20kA 2 second bushing will withstand 63kA for 1 second? Why are trying to be smarter than the client? The only time you can do that is when they are dumber than you are. Give them what they want (and are willing to pay for), otherwise when that bushing fails it will be your problem in perpetuity.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/17/2014 5:42 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/17/2014 5:54 PM

Yours doesn't have the pretty colors mine does.

Register to Reply
Power-User

Join Date: Feb 2007
Posts: 276
Good Answers: 25
#6
In reply to #5

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/18/2014 12:11 AM

Yeah, but it's "cooler"!

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#7

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/18/2014 8:19 AM

I know next to nothing about transformer bushing, but at a guess I would say the short circuit current will manifest itself as breakage (insulators?) by expansion due to heat, or melting of conductors due to heat, or mechanical stress due to magnetic forces.

Whatever the risk might be, the potential source of heat at the bush is 63kA x resistance of the bush. If the 20kA bush has much lower resistance then it might be OK heatwise.

But don't take my word for it. Being a devout coward, I would supply what the customer asked for.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/18/2014 9:44 AM

See :

IEC 60137 Insulated bushings for alternating voltages above 1 000 V ch. 4 Ratings.

__________________
Julius
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/19/2014 7:58 AM

The transformer bushings need not be rated for the system fault level. Rather, these are rated to withstand the through fault current at the bushing terminals of the secondary windings.

If through fault current is calculated from the transformer rating particulars, that could be the basis for explaining to the client.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Short Circuit Current Capacity of Transformers Bushings During a Fault

12/22/2014 12:48 AM

I agree with raghun.The transformer bushing does not have to withstand the System short-circuit current. According to IEC 60137 Insulated bushings for alternating voltages above 1 000 V ch. 4 Ratings.

If the rated loading current is 4 kA [or more] Ith=100 kA for 2 sec.

If the rated loading current is less then Ith=>25*Irated

The USA equivalent standard-I think-it is:

ANSI/IEEE Standard C57.19.00-2004

Since I don't have this standard with me I am not sure what this standard recommends.

__________________
Julius
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Ed Watts (1); horace40 (1); jack of all trades (1); lyn (2); raghun (1); RAMConsult (1); SolarEagle (1)