TTR Test on Voltage Regulator

01/25/2015 12:07 PM

Hello fellow Engineers, please what will be the cause or problem on a voltage regulator transformer.When conducting a TTR test, and the result coming is EXCITATION CURRENT TOO HIGH. the type of instrument used was MEGGER TTR 330 model.

Thank you and waiting for your contribution.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: TTR Test on Voltage Regulator

01/25/2015 2:38 PM

I guess that you couldn't make the effort to read the instruction manual where it says"...This message indicates that excitation current exceeds 500 mA. Excitation current can be reduced by using lower test voltages (40 V or 8 V)..."

While you're at it you should also the heed the message "... Read this entire manual before operating..." so that the results have some validity.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: TTR Test on Voltage Regulator

01/25/2015 2:57 PM

You'll need to explain "excitation current", or the OP will remain lost forever.

Register to Reply
Associate

Join Date: Jan 2012
Location: Tema
Posts: 25
#3
In reply to #1

Re: TTR Test on Voltage Regulator

01/25/2015 6:15 PM

Thank you RAM Consult, You ar right.The test voltage has beeb reduced to the lowest. At tap posiont 1,2and3 we had some good result but tap position four gave us nothing but high excitation current. then we changed tap to5,6 and 7. of which we had good result.after tap 8 gave us high excitation current. Later we got to know that afrer runing and testing three taps the forth gave high excitation current. The total tap positions for the voltage regulator is 65

Register to Reply
Associate

Join Date: Jan 2012
Location: Tema
Posts: 25
#4
In reply to #1

Re: TTR Test on Voltage Regulator

02/01/2015 3:17 PM

Fellow Engineers, the TTR test as been successful and it showing the transformer is good.

Register to Reply
Register to Reply 4 comments