Using 230V US VFD-drive/Motor/Pump in Australia

02/17/2015 7:10 AM

Hi, I am thinking about buying the following packaged VFD-drive/motor/pump direct from the US to use in Australia: http://www.coleparmer.com/Product/Industrial_progressing_cavity_pump_with_an_AC_VFD_drive_0_18_8_5_GPH/EW-76804-41?SearchTerm=76804-41 (I can get it here in 2-3 weeks instead of 8-10 weeks and for half the price of buying it in Australia - am short of both time and budget so on the surface seems like a good option). Since it is designed for the US, I assume it is 60 Hz, but in Australia the electricity is 50 Hz. Do you think it would still work in Australia with just a US-Australia plug adapter or am I likely to have some major problems? or would I need a secondary VFD to switch the Australian mains from 50 to 60 Hz first before it goes to the VFD-Drive packaged with the motor and pump or something like that? Many thanks, Laudrup

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Using 230V US VFD-drive/motor/pump in Australia

02/17/2015 7:37 AM

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Using 230V US VFD-drive/motor/pump in Australia

02/17/2015 7:41 AM

don't Mickey Mouse it!, forget conditioning the wave, just start out with the 50

Register to Reply
Member

Join Date: Feb 2015
Posts: 6
#3

Re: Using 230V US VFD-drive/motor/pump in Australia

02/17/2015 7:50 AM

I have already contacted them on some aspects and am waiting on a response - but if possible I was after some independent advice on whether it should work or not and the likely implications, from somebody that knows more about electrical equipment than me. People wanting to use US equipment in Europe/Australia must be fairly common and since it has a VFD on it anyway, I am not sure if it is likely to be an issue?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Using 230V US VFD-drive/motor/pump in Australia

02/17/2015 8:13 AM

Many power supply circuits are designed today to handle a wide range of voltages and frequencies. I haven't the faintest idea if this device is designed this way. I do know that if you use any product outside of where it was designed to operate, you will assume all liability. If you have an electric fire and your insurance company finds this in another part of the building they might deny your claim regardless of any effects this does or does not have on the part that started the fire.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#8
In reply to #3

Re: Using 230V US VFD-drive/motor/pump in Australia

02/17/2015 12:33 PM

Awaiting a response? Ye Gods, man! Use the telephone, for goodness'sake!

__________________
Good moaning!
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#5

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/17/2015 8:27 AM

You shouldn't have any problems, just set the parameter corresponding to the "motor base frequency" (to 50Hz) and you're ready to go, perhaps your VFD includes a parameter for "VFD supply freq." but I doubt it.

Go for it, someone's got to appreciate your efforts in cutting the leadtime and costs in a half, congrats.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/17/2015 8:34 AM

from your link..."an Applications Specialts(specialist) for additional information." you should be consulting them. and as pointed out, the motor may have choices in its menu so the frequency and voltage might just be there already, call or email

Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/17/2015 12:04 PM

Don't do or change anything, just hook it up to 230V and go. A VFD converts the AC to DC, it could not care less if it it 50Hz or 60 Hz, it just rectifies it. Then the output to the motor is recreated from that DC, so all that is necessary is that the output matches the motor. Since the motor is designed for 230V 60Hz, leave the drive set to deliver that to it, no problems.

In other words, there is no direct relationship to input frequency and output frequency whatsoever. Input power is just a raw material for making DC, then the output power is created from that DC link.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Member

Join Date: Feb 2015
Posts: 6
#9
In reply to #7

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/17/2015 4:37 PM

Thanks JRaef, great explanation, exactly what I needed to know

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#10
In reply to #9

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/17/2015 10:48 PM

Just one last "gotcha". In the US the VFD would run phase to phase. In Australia one phase will actually be neutral (which is connected to ground at the switchboard). A possible issue might be if the VFD decides that there is an input phase to ground fault because of this.

Unlikely on a small unit like this - but possible. A good question to ask.

__________________
johny451
Register to Reply Score 1 for Good Answer
Member

Join Date: Feb 2015
Posts: 6
#12
In reply to #10

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/18/2015 1:02 AM

Thanks Johny451,

I have got the actual model numbers and manuals now for both the one discussed above and for an alternative drive I am also looking at purchasing from another US supplier to go with a similar pump:

P/N:174656 - http://www.leeson.com/Manuals/SM2-SM4_071913.pdf

P/N: ESV371N01SXB http://download.lenze.com/TD/ESV__SMV%20frequency%20inverter__v18-0__EN.pdf

Do you think that these drives are likely to have the issue you mentioned? (Apologies for asking, but I don't really know which bit to look at - they both say that they are 240V Single phase 2/PE).

Thanks again

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#15
In reply to #12

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/18/2015 5:04 PM

I just had a look at both manuals and they specify 2/PE or 1/N/PE which means that they will work fine with Australian 240VAC supplies - I withdraw my "gotcha".

That comment about duty is worth considering. If you have bought stuff in before you are already aware of the cost of importing stuff, if not have a look into it. It's a real surprize if you are not expecting the cost.

The comment re insurance and Australian supply approval is also valid. Again - up to you.

__________________
johny451
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#11

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/18/2015 12:54 AM

Hi

Last time I looked you needed to have equipment that has a certificate of design for it. It the things like these are needed when your vsd catches fire and the insurance company goes around looking for somebody to pin the costs to.

And don't forget those harmonic suppression filters as your electricity network will come sniffing for. No doubt you have AMI installed because these can record the THD other thing and send alerts to the meter operator.

Cheers

Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#13

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/18/2015 8:07 AM

I would not assume that the FVD circuitry will be unaffected by the difference in input power frequency.

Call the Toll-Free Cole-Parmer Technical Support number below to get a competent answer to all your questions as well as advice on product selection for your particular application.

1-800-323-4340

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#14

Re: Using 230V US VFD-drive/Motor/Pump in Australia

02/18/2015 1:40 PM

What is the range of input voltages that the drive can take. US is 110V 60Hz. Did you clear the import duty at customs. If you have local manufacturers it will be from 50% to 100%, they will tax the drive, the motor and the pump individualy. Including the custom clearance time can add some weeks. Get the input safe Voltage range, the supply is converted to DC and the VFD circuit run independent from supply frequency on most designs.

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Register to Reply Off Topic (Score 5)
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); cristle (1); Fredski (2); JohnDG (1); Johny451 (2); JRaef (1); laudrup (3); Oomborrie (1); redfred (1); SHOCKHISCAN (1); Yahlasit (1)

Previous in Forum: Probability   Next in Forum: Animals & Wire Insulation

Advertisement