HT Capacitor

02/22/2015 6:52 AM

Resp SIr

Question regarding HT Capacitor,

1200 KVA HT (33 KV) capacitor is connected in our substation which very near (15 Mtr HT cable length) to MSEB metering system in HT switch yard.

Our actual plant load is connected 150 mtr (by HT cable) far from HT switch yard.

IF our furnace is running MSEB meter is showing 70 Amp current. (As per our electrical consultant capacitor is useful to reduce voltage spickes in HT voltage.

If our furnace is not running that time MSEB meter shows 20 Amp current & if capacitor switched off MSEB meter shows 2-3 Amp current.

SO my question is that capacitor is consuming electric power (KWH) at furnace OFF or its OK.

Awaiting your valuable replay.

Thanking you

Sagar Kalokhe

CR4 Admin: Removed phone #. From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses. You can share this information via the CR4 internal messaging system.

Register to Reply
Pathfinder Tags: HT capacitor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: HT Capacitor

02/22/2015 8:20 AM

It might but without knowing a lot of additional information I cannot tell. With all due respect, the limited information you believe is relevant that you brought us does tell me that you are not qualified to be doing anything about a substation.

Knowledge and comprehension are valuable commodities that deserve financial recognition. Hire an electrical engineer or electrician to examine your system. Let them tell you if your system configuration is wasting electric power or not.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: HT Capacitor

02/22/2015 9:42 AM

You are looking at the magnitude of the Amps without knowing the power factor angle, your kWh meter only records the real portion (kW) and is what you should be checking, it should be reading nearly the same with or without the capacitor (all other things being equal).

Here's where "thumb rule engineering" fails, someone has to pay for the I² losses that "extra" 17A are causing as they pass through the wiring, such is the penalty that you pay for having overcompensated with the capacitors, get a different more knowledgeable consultant to help you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: HT Capacitor

02/22/2015 2:55 PM

The Capacitor is normally used in Substations to improve the Power Factor. The Transformer under no load conditions will cause low PF and need correction of PF to avoid penalty from MSEB for low power factor and needs correction by adding capacitor in the system but will consumes power but if you switch off the Capacitor Low power Factor penalty will be much larger. The quantum of Capacitor to be added during no load condition will be different from that of loaded conditions depending on the type of the Furnace ( Resistance Furnace or Induction Furnace. ) The best solution is to add Capacitance by steps with the help of APFC unit depending on the value of PF you need to maintain to avoid Low Power Factor penalty by MSEB as per your contract .

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: HT Capacitor

02/23/2015 8:50 AM

The capacitor will actively oppose all inductance/inductive reactance present in the circuit when connected to it.

This means the current flow caused by reactive power will be displayed on the ammeter.

I am sure that the long length of cable connecting the substation to the oven is contributing to this.

Leaving the capacitor connected at all times will act to improve the power factor as long as there is inductive reactance present however if the circuit loses the inductive reactance the capacitor will cause power factor deviation in the opposite direction.

I would suggest you monitor the Power Factor (PF) and react accordingly.

It is possible to automate the switching of the capacitor(s) on an as-needed basis based upon the power factor (PF).

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #4

Re: HT Capacitor

02/23/2015 9:59 AM

Plausible but since the OP never mentioned anything at all about power factor, phase angle, reactive power or any of the other parameters that would indicate a good understanding of AC power, I believe your accurate words mean nothing to the OP. For all we know the capacitor could be properly placed downstream of the control switch and doubles as a snubber when disconnecting. Thus putting it out of the power circuitry when the system is OFF. The mystery 2 amperes of current could be control circuitry instrumentation, indicators or even an indication of insulation breakdown somewhere.

To find out what is going on requires a knowledgeable person, on site, with wiring documentation to troubleshoot the situation. The OP is clearly not a knowledgeable person. Neither you nor I are on site of this operation. As far as documentation, well nobody has mentioned anything about that until now.

__________________