how to calculate multiplying factor if meter ctr is -/5?

02/26/2015 6:09 AM

hi,

what is the multiplying factor for 3 ph 4 wire kwh meter if line ctr is 1000/1A, ptr 3*240V and meter ctr is -/5 A, ptr is 3*240V?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: how to calculate multiplying factor if meter ctr is -/5?

02/27/2015 6:33 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: how to calculate multiplying factor if meter ctr is -/5?

03/23/2015 7:52 AM

Let's say the primary current is 1000 A. Then the meter receives 1 A and interprets it as 1000 A.

Now, if CT ratio will be 1000/5 and the primary current will be 1000 A too, the meter receives 5 A and interprets it as 5000 A. So, in this case you have to divide the reading by 5.