Transformer Turn Ratio Testing

03/02/2015 8:14 AM

Dear all,

We have conducted turn ratio test on some distribution transformers rating 250 - 1000 KVA. While analyzing test results we found that phase displacement in few transformers is as below.

A B C

TR # 1 Phase (min) -89.88 30.09 150.08

TR # 2 Phase (min) 210.13 210.13 210.13

I want to know what is the admissable / acceptable range of phase displacement, I mean any thumb rule to consider it pass/fail. I shall try to explain more my question in other way, are the above results are Ok or not?

Please note that all the transformers are in service.

Thanks to all,

Manzoor

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Transformer Turn Ratio Testing

03/02/2015 9:00 AM

Power Transformer Turns Ratio Test | EEP

Depends on the specification.

Register to Reply
2
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: Transformer Turn Ratio Testing

03/02/2015 12:33 PM

Your question doesn't make sense. If the outcome of the test were unacceptable, then those transformers would have been removed from service!

Why are you carrying out a "test" if you don't know where your boundary between acceptable and unacceptable lies? That doesn't make sense to me either. How can you test, if you don't know what you're testing for?

__________________
Good moaning!
Register to Reply Good Answer (Score 2)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Transformer Turn Ratio Testing

03/02/2015 1:46 PM

See previous threads by Manzoor14, it ain't just transformer testing he has been asking about.

Rather disturbing if you ask me, what's the point of paying a company to test high voltage transformers, cables and switchgear if they don't know what they are doing and have to ask us.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Transformer Turn Ratio Testing

03/02/2015 2:10 PM

It's not ethical, honest or SAFE!

Imagine this conversation.

Customer: "Manzoor14, the switching station your company maintains for us exploded, killing three people." Our lawyers will need all your professional licenses, permits certifications indicating that you are qualified for your job, all the signed documents certifying the load calculations, EHV cable testing, LV breaker testing, over current relay selection and certification documentation, Hi-pot test results and certification and MV switchgear grounding test results and certification. Today."

Manzoor14: "Well, those will have to be procured from our test and certification supplier, CR4." I'll get right back to you.

Customer: "who is your contacts there?'

Manzoor14: "Del the Cat, Crabtree, tcmtech, jack of all trades, redfred are a few, sir"

Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5
In reply to #4

Re: Transformer Turn Ratio Testing

03/02/2015 2:22 PM

Indeed, given Manzoor14's previous threads it does appear to me he is acting unethically.

Others on CR4 can make up their own minds and should do so before offering help on CR4 in general (we ain't talking about baking cakes you know), but isn't that what we should always be doing least our help results in someone's death because someone was trying to do something the were not supposed to do but we gave them the tools or knowledge to do it?

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: Transformer Turn Ratio Testing

03/03/2015 5:43 AM

It's just giving them the tools and knowledge to harm themselves differently is all. Some cautions may be heeded or not.

Think of CR4 as a "fast forward" button.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Off Topic
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #6

Re: Transformer Turn Ratio Testing

03/03/2015 1:40 PM

So if we were talking about something more extreme like advising on building a bomb, performing and surgical operation or laundering money that would also be fine. All these things are unethical also just as (for example) helping someone do something potentially dangerous they are not qualified to do while they get paid to do it.

We have had plenty of that on CR4, clueless people trying to design pressure vessels, do their own high voltage wiring or specify electrical equipment for customers even though they appear to have no electrical experience, etc.

Consultants do it all the time but there are fine lines and grey areas, they (generally) are qualified in said areas and take the risks when they sign off on the end design for example.

Something to think about. A balancing act between the fine lines and grey areas.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #8

Re: Transformer Turn Ratio Testing

03/03/2015 10:59 PM

If telling somebody who is unqualified or inept how to perform a task, where these attributes don't help at all, makes that somebody realise that they should get somebody else to release the smoke then...mission accomplished.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #9

Re: Transformer Turn Ratio Testing

03/03/2015 11:19 PM

Unfortunately, when somebody like you tells "somebody who is unqualified or inept" how to perform a task, and they kill some innocent bystander trying to do it anyway, who is to blame?

YOU are!

When you tell someone that you recognize as somebody who is unqualified or inept how to perform a task that you know they should not do, you become an accomplice to the aftermath.

Your comment, "giving them the tools and knowledge to harm themselves" is disgusting and irresponsible.

You have no business here.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11
In reply to #10

Re: Transformer Turn Ratio Testing

03/04/2015 12:06 AM

The ..."tools and knowledge"... comment came from #5. I just ran with it.

Of course I have no business here.

You are right.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7

Re: Transformer Turn Ratio Testing

03/03/2015 8:50 AM

TTR results are based upon the transformer windings design and the testing method being used.

It is not possible to accurately answer your questions via this forum.

Given your statement that all of the transformers are currently in service it is not feasible that there is anything critically wrong with the TTR otherwise the output voltage would be skewed and all equipment attached to the transformer(s) load side would be experiencing issues and/or failure.

I strongly suggest you contract with a reputable transformer testing vendor to analyze your testing method and results.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); jack of all trades (3); lyn (3); SHOCKHISCAN (1); Wal (3)