Editor's Note: CR4 thanks Dick Cawley of GEA Consulting for contributing this blog entry.
Copeland Bulletin AE4-1331 R3 covers the need to ensure that adequate lubricant always remains in the compressor sump. For instance, they recommend the addition of 1 oz oil for every five (5) lb of refrigerant over 20 lb of refrigerant charge.
A scroll compressor is equipped with about 65 oz lubricant charge. One can quickly calculate the lubricant residing in a system having, say, and 1% lubricant in refrigerant. If the system has 20 lb of refrigerant, the oil in continuous circulation (away from the compressor) would be 20*.01 = 0.2 lb, or 3.2 oz. A system charged with, say, 50 lb refrigerant would have 8 oz lubricant in circulation. This is a substantial portion of the oil charge (12.3%) that cannot be in the sump. Six (6) oz. additional oil, as recommended by the compressor manufacturer, is needed in the system. Note, too, that these calculations are for steady state operation. Many times during transient operation, the circulation rate can be higher, which emphasizes the need for sufficient run time after the compressor is started.
Stay tuned for more...
- Dick Cawley
Re: Understanding Oil Return in Refrigeration Systems (Part 6: Maintaining an Adequate Lubricant Level)
04/14/2011 8:06 AM
Once again, this geanorm blog brings forth good and well-explained information.
04/14/2011 8:36 AM
Thank you Tornado. Your positive comments, when material justifies it, encouages the GEA Consultants who are very experienced in HVAC technlogy but new to the blogging forum.
geanorm
04/14/2011 9:03 AM
I think you are doing a good job with this blog series. It concentrates on information from many sources without being overtly commercial. I'm in industrial ammonia refrigeration rather than HVAC, and have briefly encountered GEA screw compressors. This was a few years ago, at either or both of FES and M&M (I was in York, PA at the time, and toured both factories.)
04/14/2011 9:18 AM
Actually Tornado we are not the manufacturing company "GEA" that I beleive you are referring to. GEA Consulting is a group of mostly past Trane engineering and business leaders now providing consulting assistance, primarily to the HVAC industry. Non the less, we are happy you find merit in the matreial we post.
Kind Regards,
geanorm
04/14/2011 11:18 AM
You're right; I did not realize that these were different entities. I will of course stay tuned to your continuing posts.