For a small substation (30mx30m) where soil resistivity is higher around 1000 ohm top layer and fault current 7kA, is it possible the measured step potential 2m outside substation could be higher value than measured touch potential inside sub

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: measured Touch and step potential

03/19/2015 4:16 AM

Yes.

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: Measured Touch and Step Potential

03/19/2015 11:05 AM

Yes, depending on the system and where the fault is located in reference to the substation.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3
In reply to #2

Re: Measured Touch and Step Potential

03/20/2015 1:52 AM

Where the fault is, is the thing.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Measured Touch and Step Potential

03/20/2015 2:05 AM

In my opinion, the earth potential in outside area of a substation decreases very fast with the distance from the fence.

The step potential is the potential difference between two points on the earth and could be higher than the step potential measured inside the fence where the earth potential-nevertheless high- could be more uniform. The touch potential is measured between the grid and a point on the earth and this difference could be very high [similar to transferred potential].

__________________
Julius
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Crabtree (1); SHOCKHISCAN (1); Wal (1)

Previous in Forum: Time Delay Relays   Next in Forum: 220V Low Voltage Ship Supply

Advertisement