220V Low Voltage Ship Supply

03/19/2015 7:39 AM

Hello,

I am curious as to how the electrical distribution system works for low voltage applications such as lighting on board a vessel. My understand is that 3 phase 440v is transformed down (delta-delta) to 3 phase 220v and then two of the 'live' wires are used to power the required applications.

Does this mean that the system is now a two phase system and the two phases are 180degrees out of phase? and would there now be 110v from phase to earth and 220v phase to phase?

Any clarification would be much appreciated

Thanks

Register to Reply
Pathfinder Tags: ship lighting system
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: 220V Low Voltage Ship Supply

03/19/2015 8:21 AM

Have you read all you can in Wikipedia on this topic, Mildred?

You don't use the earth conductor for carrying current except during clearance of a fault. The answers to your questions are that, no, live to live is a single phase arrangement and they are not 110v to earth.

__________________
Good moaning!
Register to Reply
5
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: 220V Low Voltage Ship Supply

03/19/2015 11:02 AM

No, the two phases would not be 180 degrees out of phase.

If the transformer is Delta-Delta the displacement would be 120 degrees.

The voltage would not be 110V to ground because there is not a ground reference in a Delta-Delta system unless one of the phases is tapped for metering and protection.

In a Delta-Delta system with a corner ground (one phase grounded) the voltage readings would be 220V-to-ground on one ungrounded phase, 220V-to-ground on the second ungrounded phase, and 0V-to-ground on the grounded phase.

The voltage phase-to-phase would be 220V.

The terminology used depends on who and where you are and may be "single phase" or "two phase".

Normally lighting and outlet service power is provided by a Delta-WYE transformer with a grounded neutral attached to the "Star" point. (4 wire or 5 wire distribution system wiring depending on application code requirements.)

Wikipedia has an excellent explanation of this subject.

Please donate and support Wikipedia as much as possible so that we do not lose this wealth of information.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Good Answer (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: 220V Low Voltage Ship Supply

03/19/2015 4:46 PM

Amen....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#7
In reply to #2

Re: 220V Low Voltage Ship Supply

03/19/2015 11:21 PM

GA from me too.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#4

Re: 220V Low Voltage Ship Supply

03/19/2015 5:33 PM

220 V is low voltage?

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5
In reply to #4

Re: 220V Low Voltage Ship Supply

03/19/2015 7:24 PM

Yes. So?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#6
In reply to #5

Re: 220V Low Voltage Ship Supply

03/19/2015 10:32 PM

No so! Here yes so!

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10
In reply to #4

Re: 220V Low Voltage Ship Supply

03/20/2015 11:03 AM

Only by those that the skin has been toughened by salt water over a long period of time.

Actually low voltage is classified as any voltage less than 600V.

SAFETY BLURB: New NEC and OSHA regulations. require LV gloves be worn when working on any voltage greater than 50V.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: 220V Low Voltage Ship Supply

03/20/2015 6:41 AM

You asked:-

Does this mean that the system is now a two phase system and the two phases are 180degrees out of phase? and would there now be 110v from phase to earth and 220v phase to phase?

In my Navy time, we transformed from 3 Ph. 440VAC (NATO Navy power standards) down to 120VAC phase to phase (if I remember correctly), for all domestic power and lighting. A Star/Delta transformer if I remember correctly.

Power is taken off across a single Delta field winding (if memory serves me!), between any two of the three connections L1, L2 and L3. My take is that its a single field and therefore a single phase.

Its a long time since I was in school for power Generation!!!

We never ever used a neutral.....simply not needed. 3 Phases and ground (the ship's hull....)

In my time, on 220VDC ships, the whole ships power was 220VDC for everything. Its also far less dangerous to life and limb.....(that will get someone "up in arms", but its true....!)

What is current (pun intended!) today I cannot say......Hopefully there is someone here more up to date....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Mar 2015
Posts: 3
#9

Re: 220V Low Voltage Ship Supply

03/20/2015 9:58 AM

Thanks for all of the input, I have been looking at some material. I found a drawing of what i am trying to explain i have attached it.

With reference to the drawing what would be the voltages provided to the circuits? I don't know how to calculate them, will some cancel due to different phase angles therefore it would be 110V?

I am also confused by what the circuit reference will be if both wires are 'hot' is there no reference and when one wire is positive the other is negative.

If these questions are stupid i apologise i have tried to read on my own some but i cant seem to gain the information i need.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#11
In reply to #9

Re: 220V Low Voltage Ship Supply

03/20/2015 11:27 AM

All that circuit does is transform one set of RST in delta to a different voltage RST in delta. There is no earth reference, so your phase to earth voltages could be anything.

Positive and negative have little meaning in an ac circuit other than to look at something at any instant in time. Your voltages are alternating some tens of times a second. Nuff said?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#12
In reply to #9

Re: 220V Low Voltage Ship Supply

03/20/2015 5:13 PM

The voltages across each of those separate single phase supplies will be 220v RMS, you will not see 110v anywhere there.

Google RMS voltage for more info on that term.

Some folks claim that because there are actually 2 phases then it should be called a 2 phase supply, but in reality, there is only one resultant sine wave voltage present, and so while single phase is arguably a better fit, the debate goes on.

As there is no earth connection to the transformer secondary then there is no earth reference for any of the live conductors.

A bit of reading on isolation transformers may assist you.

The common arrangement for achieving earthing and neutral is to have a star connected secondary with the star point connected to ground, but often a delta secondary is corner connected or even connected in high leg configuration.

Google those terms for more on the subject.

Register to Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#21
In reply to #9

Re: 220V Low Voltage Ship Supply

03/24/2015 12:51 PM

It's been a very long time for me since I sailed as Electrical Third but I seem to remember that with a Star winding from the center to each leg is based on 1.73. That is that each leg in a 220v system from center to end of leg would be 220 divided by 1.73 or 127 volts. All three legs should be feeding separate transformers and legs nearly of equal loads to keep a balanced situation.

__________________
Spinco
Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#13

Re: 220V Low Voltage Ship Supply

03/20/2015 7:42 PM

You never, ever, never ground a shipboard electrical system

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#14
In reply to #13

Re: 220V Low Voltage Ship Supply

03/20/2015 9:59 PM

I think you may find yourself at odds with a number of authorities on that point.

Here's one Australian Maritime Safety Authority. See section 2.13 and particularly 2.13.1.2.2

Here's another DNV ship/HLSC electrical rules See section D400.

And another See section 2.1.4

Or this one Section 10.6.7

Or the Norwegian maritime authority See sections 3, 4 and 5.

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#15
In reply to #14

Re: 220V Low Voltage Ship Supply

03/20/2015 10:43 PM

shipboard electrical are floating grounds, no pun intending. Both black and white have voltage. Voltage will be measured to ground via capacitive coupling. If the hull were grounded, electrolysis would occur, in addition the hull could become charged posing a shock hazard to anything in the water

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#16
In reply to #15

Re: 220V Low Voltage Ship Supply

03/21/2015 1:58 AM

"in addition the hull could become charged posing a shock hazard to anything in the water"

I'm guessing that comment refers to when the vessel is connected to shore power as no such danger could exist if it were not.

So I will attempt to address the shore power issue only.

As seen by a person in the water, a ship's hull when connected to shore power becomes simply another class 1 single insulated appliance.

If this hull is not earthed and there is a sufficient leakage current to the hull due to failed insulation on the ship or similar cause, there will be a current flow back from the hull to the shore power main earthing conductor or to the general ground mass via the water (the shore power supply is referenced to that earth). Either way, the swimmer is in danger of electrocution.

Similarly, any person touching both the hull/superstructure and a grounded item on the pier, such as a gantry or the like would also be in peril.

Were no earth bond installed, an RCD may provide protection if there is one in place and working correctly, but the timely operation of an RCD even at 10mA is no guarantee of safety for a swimmer as, while the device may operate in time to prevent electrocution, the victim may be incapacitated for long enough to drown as many more vital organs can be traversed by the current due to the body's immersion.

Bonding of the hull to the shore power earth eliminates all of these concerns as the hull and earth are held at equal potentials and the mains breaker or RCD will operate if there is a fault detected.

It is for these reasons that bonding of the hull to earth is mandatory when connecting to shore power.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#17
In reply to #16

Re: 220V Low Voltage Ship Supply

03/21/2015 4:26 AM

I'll repost that reply as I omitted a couple of key words that will make a difference to the intention. The changes are underlined for clarity

"in addition the hull could become charged posing a shock hazard to anything in the water"

I'm guessing that comment refers to when the vessel is connected to shore power via direct connection as no such danger could exist if it were not.

So I will attempt to address the shore power issue only.

As seen by a person in the water, a ship's hull when directly connected to shore power becomes simply another class 1 single insulated appliance.

If this hull is not earthed and there is a sufficient leakage current to the hull due to failed insulation on the ship or similar cause, there will be a current flow back from the hull to the shore power main earthing conductor or to the general ground mass via the water (the shore power supply is referenced to that earth). Either way, the swimmer is in danger of electrocution.

Similarly, any person touching both the hull/superstructure and a grounded item on the pier, such as a gantry or the like would also be in peril.

Were no earth bond installed, an RCD may provide protection if there is one in place and working correctly, but the timely operation of an RCD even at 10mA is no guarantee of safety for a swimmer as, while the device may operate in time to prevent electrocution, the victim may be incapacitated for long enough to drown as many more vital organs can be traversed by the current due to the body's immersion.

Bonding of the hull to the shore power earth eliminates all of these concerns as the hull and earth are held at equal potentials and the mains breaker or RCD will operate if there is a fault detected.

It is for these reasons that bonding of the hull to earth is mandatory when connecting to shore power if an isolation transformer is not used.

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#18
In reply to #14

Re: 220V Low Voltage Ship Supply

03/21/2015 9:17 AM

Very fine articles indeed. Page 14 of the Australian Maritime Safety Authority states that earthing for both AC and DC systems may be isolated and if so the steps taken to install them.

So we are both correct, but for safety of passengers, crew and hull, I prefer isolated "floating" systems.

There have been more than a few instances where swimmers have been electrocuted, both in marinas by faulty/defective wiring of adjacent ships, and along side boats with generators running.

As for using the hull for a DC return, that can lead to serious electrolysis, as well as interrupting the settings of a cathodic protection system. While the negative terminal is connected to ships hull nomimally through the engine block, a separate lead should be installed to prevent the hull from becoming a conductor.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#20
In reply to #18

Re: 220V Low Voltage Ship Supply

03/21/2015 6:58 PM

There is really no such thing as an isolated hull, there will always be high impedance and capacitive couplings, and if that coupling becomes of sufficiently low impedance then shocks can occur.

The real problem with an isolated system is the necessity to detect and clear first ground faults as soon as possible. While the first one is not dangerous in itself, if it were to go uncleared and a second fault occurred in another phase or even in the other conductor of the same phase, then a fatality is possible.

While effective earth monitoring systems are generally employed on these vessels, the very fact that the first fault causes no inconvenience tends to make the operators complacent and slow to correct the fault.

Swimmers have been electrocuted in marinas due to incorrect use of earth bonding conductors or isolation transformers. An isolated hull with a first fault and no isolation transformer or earth bond to the shore can kill a swimmer. If the hull were using the IT earthing system that could not happen.

Again I make the point that the hull is not to be used for return currents, and have never said that it should be. The connection to the hull at one point only of the earth in an AC system, and the negative of a DC system will not cause any current flows or increase electrolysis in the hull.

I guess we will agree to disagree on this subject, but good debate anyway.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #14

Re: 220V Low Voltage Ship Supply

03/21/2015 3:53 PM

For me, none of your links worked.....with or without the "S".

As far as I remember, earthing a supply connection on a ship is considered an error and will need to cleared.

To "sense" these errors, a connection is made to ground via a low wattage bulb on each phase. When an earth fault occurs somewhere, the lamp will then light, the switchboard operator then needs to do some simple checks to find the area within the ship and send the electrician to the right area....

But I have never seen any other "deliberate" methods of grounding....possibly due to possible accelerated corrosion or something!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Mar 2015
Posts: 3
#22

Re: 220V Low Voltage Ship Supply

04/12/2015 7:50 AM

Some good information here thank you. I suppose my question essentially was why, when using a meter to measure between ground (ships hull) and one of the live wires of the single phase, do we get a voltage of 110v.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23
In reply to #22

Re: 220V Low Voltage Ship Supply

04/12/2015 8:26 AM

to answer your question:-

"Because neither are connected to the hull...."

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (3); Crabtree (3); IdeaSmith (1); JWthetech (3); Rixter (1); SHOCKHISCAN (2); SolarEagle (1); spades (6); Spinco (1); TheYawning (2)

Previous in Forum: Measured Touch and Step Potential   Next in Forum: Connecting P1 and P2 NC Motor Thermostats to Drive

Advertisement