CBCT Connection

03/21/2015 4:31 AM

Is it required to take neutral cable through CBCT along with RYB cable.

i think RYB is enough?ryt? if no correct me.

Register to Reply
Pathfinder Tags: CBCT
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: CBCT Connection

03/21/2015 6:10 AM

ryt.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: CBCT Connection

03/21/2015 7:33 AM
__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: CBCT Connection

03/21/2015 11:08 AM

ryb ?

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: CBCT Connection

03/21/2015 12:11 PM

Three phases. Should be "cables". Neutral needed in case loads aren't exactly balanced.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: CBCT Connection

03/21/2015 12:14 PM

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#6

Re: CBCT Connection

03/21/2015 3:32 PM

The problem here is interpreting these TLAs and FLAs.

__________________
paulusgnome
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#7
In reply to #6

Re: CBCT Connection

03/21/2015 7:19 PM

We haven't heard from Anonymous Hero yet, he's from FLA.

Register to Reply Off Topic (Score 5)
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#8

Re: CBCT Connection

03/22/2015 5:40 AM

If there is a difference between the three phases, a neutral current will flow. There will be an imbalance in the RYB

The fourth, neutral cable must pass through the residual current detection. If there is then an earth fault, there will be an imbalance to operate the protection.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#9

Re: CBCT Connection

03/22/2015 6:30 AM

Do you have access to your national wiring standard? If so, read it. If not, then why not?

__________________
Good moaning!
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#10

Re: CBCT Connection

03/22/2015 11:20 AM

All four conductors have to pass through the CBCT. You don't want unbalance to trip the ELCB. Only earth leakage. That will happen only if the vector sum of the entire current is zero normally. Any earth leakage will make the vector sum no longer zero, so the ELCB (or RCD/ RCBO) trip. This is the reason that it is called "Core-Balance-Current-Transformer"

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11

Re: CBCT Connection

03/22/2015 2:55 PM

Not sure what a CBCT is (I doubt your working on dentistry scanners). Circuit breaker current transformer perhaps?

I don't know what type of electrical and grounding system you have so cannot say (they vary from country to country and even state to state).

Refer to your local Indian electrical standard and electrical codes of practice, the answer will be in there.

__________________
jack of all trades
Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#12

Re: CBCT Connection

03/23/2015 6:01 AM

A simple reply is:

if there is a neutral conductor (TPN or 4-wire supply) - Yes.
if there is no neutral conductor (TP or 3-wire supply) - No.

Any protective earth continuity conductor should be outside the CBCT

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#13

Re: CBCT Connection

03/23/2015 10:39 AM

Their are specific requirements in various electrical codes for switching the neutral. You probably need to consult with a local electrician who knows the local requirements. Most of the time you do not switch the neutral in most codes, but again codes vary. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply Score 1 for Off Topic