Increasing NPSHa

07/11/2007 8:48 AM

How can i increase NPSHa in a cooling water system.

In our design NPSHa is 7m but NPSHr is 10m.

Purchaser had said at first that NPSHa is ample!but now he says they can increase it up to 7m! in this case capacity is about 3000 m3/h

please help me

Register to Reply
Pathfinder Tags: NPSH
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Increasing NPSHa

07/11/2007 11:29 AM

How can i increase NPSHa in a cooling water system.

What scope is there for extending the pond walls upwards and increasing the water level?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: Increasing NPSHa

07/11/2007 5:33 PM

That's a lot to increase NPSH but an inducer may help.

Register to Reply
Associate
South Africa - Member - ShoSholoza Engineering Fields - Mechanical Engineering - New Member Popular Science - Weaponology - New Member

Join Date: May 2007
Location: South Africa
Posts: 44
#3

Re: Increasing NPSHa

07/12/2007 1:52 AM

Can you simplify the piping to the suction thus reducing frictional losses e.g fewer bends?

Is it possible to position these pumps below ground level [in a pit] and thus obtain the additional NPSH [I had to do this recently, as the conventional condensate extraction pumps were too costly]

__________________
Can you imitate yourself?
Register to Reply
Power-User

Join Date: Feb 2007
Location: Aberdeen, Scotland
Posts: 393
Good Answers: 21
#4
In reply to #3

Re: Increasing NPSHa

07/12/2007 6:53 AM

Or increase the size of the pipes on the suction end.

Sounds like some pretty big pumps so getting more suitable pumps is probably out of the question? Pipes are expensive too but just a thought anyway.

Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Increasing NPSHa

07/12/2007 7:09 AM

NPSHa can be incresed by reducing the frictional losses in the pipe or discharge should be below the suction level. if your suction side above the water level then it can also helping to incresing the NPSHa

Register to Reply
Anonymous Poster
#6

Re: Increasing NPSHa

07/12/2007 7:54 AM

Sounds like you need a submereged suction pump of slightly more capacity and slightly more head then the npsha delta. A better description of the task would be nice. Typically all of the bad crap happens to a pump on the suction side for that reason the design of any system should allways advantage the suction side of the pump. If you are recirculating from a pond then put the pump in the pond. If you have a loop, put in a 24 inch dia. vented stand pipe and put the pump in it. In each case submerge the pump in a vented suction application.

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Increasing NPSHa

07/12/2007 8:00 AM

oops Since it will take a 24" verticle turbine or so ....use at least an 8ft dia. stand pipe or tank. Anything else is a gamble.

Register to Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#8

Re: Increasing NPSHa

07/15/2007 1:49 AM

Try to measure the water level above suction line of pump. NPSH is 7 Meters mean theoretically you can lift water from a depth of 7 meter- friction loss. from the pump.Also this is mentioned is the design catalogue of pump. Some how increasing the pipe size will but I feel if the design can not change , you have to submerge the pumps 3 meters down looks like submersible pumps.

You have to define the problem in details- water level, pump suction level. groud level etc.

__________________
Best Regards, Shivaram
Register to Reply
Associate

Join Date: Jun 2007
Location: Colombia
Posts: 44
#9

Re: Increasing NPSHa

07/16/2007 9:43 AM

Depending on the system you have, it would be possible to do one or more suggestions posted above. Since you are the only one who knows the configuration, could you provide further information details?

Maybe will be easier if you try with other pump which has the adequate NPSHr (NPSHr>11m). Normally this is the way to do that.

SaC.

Register to Reply