Hi guys,
I was doing my quarterly electrical testing of one of our local asphalt plants.
The installation is monitored and controlled via an Astec system supplied by an American mob.
The plant runs off a large gen set at 50hz and the plant is designed to run at 50hz.
The plant is new and has been tested only once before this by myself with no issues. This test run I came to a light and power distribution panel that has 10 Mod 6 NHP single pole RCD/MCB combo's.
All of these breakers passed the first test 3 months ago and now this test 9 out of 10 failed to trip via an induced fault and failed to trip with the test button.
In 10 years I have done a lot of RCD testing and never seen that many fail in that manner in such a short period.
Any one had a similar experience or thoughts on this issue?
I have since replaced all the breakers with 20amp single pole Schneider rcds and am hoping not to have to replace them under warranty by next test?
Cheers
Good Answers: 804
Re: NHP Mod 6 RCD's
03/25/2015 5:14 AM
NHP is a large distributor in Australia, not a breaker mfr. The breakers that they sell with their own name on them are actually made by Teresaki of Japan. I have never been impressed with the quality of Teresaki breakers of any sort, I can only imagine that their line is MCBs are among the lowest of low.
Being that NHP branded breakers are not sold outside of Australia and New Zealand, I can imagine it likely that the control equipment was made there, despite Astec being an "American mob".
Good Answers: 122
Re: NHP Mod 6 RCD's
03/25/2015 9:15 AM
Many MCB units are designed and warranted to interrupt a fault at maximum current rating one (1) time.
Not knowing what type of test you are performing nor the breaker interruption rating nor the current level used for testing it is possible that your test voltage and/or test current level is too high.
Acceptance testing should only be performed once during the life of the MCB at installation and all tests after initial should at reduced test values as per OEM guidelines.
In my opinion replacing the NHP breakers with Siemens equipment is definitely a step in the right direction.
New Zealand - Member - Kiwi
Good Answers: 29
Re: NHP Mod 6 RCD's
03/26/2015 2:38 PM
All MCBs and RCDs sold in Australia and NZ are subject to type approval, which helps ensure that they are at least up to the standards that are in place.
This may not necessarily apply to units supplied via a US supply chain.
If you want to get to the heart of the problem, you need to test the RCDs with a proper RCD tester that measures both trip times and trip currents.
paulusgnome
Good Answers: 102
Re: NHP Mod 6 RCD's
03/27/2015 6:51 AM
Never seen that many all go bad at one time, a very short time, either.
I have to contend with cheap Chinese knock offs here and they are more reliable than that.
Surely a warranty claim is in order.