Do 4-20ma Can Be Superimposed On RS-485 Cable

03/25/2015 12:54 PM

Do 4-20ma can be superimposed on RS-485 cable, I have seen a datasheet they are using a ultra-sonic multipath transmitter, the output signal is Rs-485 serial interface 4-20ma HART superimposed, do its possible, if possible how come 2 signals data can be retrived. the communication protocaol is Modbus RTU.

output signal: RS-485 serial interface

4-20ma HART superimposed

output reading: flow rate.

serial comm port: rs-232, rs-485

communication protocaol: modbus RTU

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: do 4-20ma can be superimposed on RS-485 cable.

03/25/2015 1:09 PM

Instead of waiting, you could pick up the phone and talk it through with the equipment supplier, Mildred. It seems people are frightened to do that these days.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#2

Re: do 4-20ma can be superimposed on RS-485 cable.

03/25/2015 2:10 PM
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Do 4-20ma Can Be Superimposed On RS-485 Cable

03/25/2015 2:49 PM

No, 4-20mA is not superimposed on the RS-485 line or vice versa.

There are multiple, separate, individual connections on this device.

One connection is 4-20mA HART (yes, HART is an FSK signal superimposed on the DC 4-20mA). Its connections will have a (+) and a (-).

A second connection is RS-232, which supports Modbus RTU. It will like have a Rx, Tx and a signal ground.

A third connection is RS-485, which supports Modbus RTU. It will likely have a connector with A, B and signal ground.

The 4-20mA does not mix with either the RS-232 or RS-485.

Register to Reply
Associate

Join Date: Mar 2015
Location: Iraq- hot Middle East
Posts: 30
#4

Re: Do 4-20ma Can Be Superimposed On RS-485 Cable

03/25/2015 3:52 PM

(4-20 )mA it is not superimposed on any RS(232/485)it is superimposed on (FSK) frequency shift keying to make up (HART communication protocol) if you want to communicate between (4-20mA.HART) device and your PLC(control) or p.c use on of these adapters converters FXA191 FXA193 FXA1195 via RS232/usb ports .to make a control orders regarding with

RS232 or RS485 in your flow rate they are for operation software program that comes on a disc and installed in your P.C it is just to monitor not to handle (4-20mA.HART).for read or write data.

good luck .

Register to Reply
Commentator

Join Date: May 2011
Posts: 91
#5

Re: Do 4-20ma Can Be Superimposed On RS-485 Cable