Sizing Neutrals Single Phase Distribution

03/27/2015 3:54 AM

With increasing non linear loads in residences will it not be prudent to have incoming 4 pole breakers with neutral rated for 2 times than phase contacts to avoid floating Neutral conditions due to failure or burnout of neutral contact/conductor.

Register to Reply
Pathfinder Tags: House wiring
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Sizing Neutrals Single Phase distribution

03/27/2015 4:08 AM

Think about it. The neutral current can never be greater than the largest of the three phase currents.

Follow the wiring regulations applicable to your country and don't waste time trying to reinvent the wheel.

__________________
Good moaning!
Register to Reply Score 1 for Off Topic
Member

Join Date: Jul 2010
Posts: 9
#2
In reply to #1

Re: Sizing Neutrals Single Phase distribution

03/27/2015 4:31 AM

I think you have not experienced the problem of Neutral over heating due to Triplen Harmonics in Single Phase circuits where computer or other linear loads are predominant and we have to provide 3P+2N cables and Busducts as the currents in Neutral circuit can be as high as 1.732 times phase currents.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: Sizing Neutrals Single Phase distribution

03/27/2015 5:07 AM

And I think you're not talking about residences any more. Instead of coming here, why don't you convince someone your country's wiring regulations need amending instead? Your ball.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#4
In reply to #1

Re: Sizing Neutrals Single Phase distribution

03/27/2015 5:21 AM

Actually it can. Triplen or zero sequence harmonics due to the use of non-linear loads such as switch mode power supplies, electronically ballasted fluorescents, VFDs, etc. can result in high currents circulating in the neutral.

Zero sequence harmonics, ie, 3rd, 6th, 9th, are in phase and therefore add up in the neutral conductor. The neutral current can thus be 2 to 3 times higher than the largest line current, and if the neutral conductor is of insufficient capacity, the resultant voltage drop can cause overheating of the conductor, burning of switch contacts and a potential difference between neutral and earth.

Balancing of loads between phases does little to alleviate this problem and the use of voltage optimisers, zig zag transformers, filters, etc. can be necessary.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5
In reply to #4

Re: Sizing Neutrals Single Phase distribution

03/27/2015 5:32 AM

OK. So I've got three single phase breakers of 32A rating, and two of them are turned off. There is 32A in the phase, meaning that the breaker is at the point of tripping. What is the neutral current?

I then turn on the other two breakers, which each load to the same 32A. What is the neutral current now?

Provided there is a neutral current, there will always be a voltage between it and ground.

Your ball.

__________________
Good moaning!
Register to Reply Score 1 for Off Topic
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6
In reply to #5

Re: Sizing Neutrals Single Phase distribution

03/27/2015 7:04 AM

Perhaps I should have said a "greater" potential difference or even a "dangerous" potential difference between neutral and earth, but I thought the implication was obvious when taken with the context of my accompanying statement re. neutral conductor sizing.

Depending on the dynamics of the loads, the neutral current can be considerably higher than the 32 amps due to those harmonics that I mentioned.

As for being "my ball"...I have stated plain facts, whether you choose to believe them concerns me not.

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#13
In reply to #4

Re: Sizing Neutrals Single Phase distribution

03/31/2015 9:26 AM

I have not had a problem with high neutral currents that I know of. No problems with neutral wires or connections. But to be ready to check for them, can they be measured with normal clamp on amp meters, or is a power quality analyser needed? -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#14
In reply to #13

Re: Sizing Neutrals Single Phase distribution

03/31/2015 7:05 PM

A digital analyser is the best option, but if your clamp meter is a true RMS type then it can be used. Average measurement AC ammeters - even those calibrated to display RMS values - will only satisfactorily measure sinusoidal waveforms and are pretty much useless on non-linear ones which will be the case for neutral harmonics.

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#15
In reply to #14

Re: Sizing Neutrals Single Phase distribution

04/01/2015 1:20 PM

Thanks. I know my DMM is true RMS, but I'll have to check the speccs on my clamp meter. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#16
In reply to #1

Re: Sizing Neutrals Single Phase distribution

04/10/2015 3:53 AM

Dear Mr.Crabtree,

You are right, the Neutral Current can never be more than the highest current in any one of the phase.

But the Non-Linear Load which is responsible for Harmonic Disturbances, the amplitude of the different Harmonics will add up ARITHMATHICALLY and NOT VECTORIALLY, as against the conventional circuit where the unbalanced current will flow through Neutral for which the resultant current is VECTORIALLY ADDED, and hence neutral conductor size will e less.

Hence it is essential to have higher size Neutral Conductor, prepferably independendant earthing for each non-linear loads. This topic came for discussions some time back.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#7

Re: Sizing Neutrals Single Phase Distribution

03/27/2015 9:34 AM

A contractor can always put in heavier gauge wire of phase, neutral or ground than the code specifies as minimum standard. Remember though that the nominal conducting material, copper, is not cheap. It is so valuable that most coins are no longer made with copper. If the customer/contractor can afford and desires heavier gauge wire than the minimum standard, great.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: Sizing Neutrals Single Phase Distribution

03/27/2015 11:12 PM

Upsizing the neutral would seem very prudent it seems.....

The present, code sanctioned practice of having downsized neutrals in nominally balanced 3ph distribution networks may need reviewing.

I haven't seen the insulation on the smaller neutral conductor on the local utility's ABC that runs past my balcony blistering yet. There may be a neutral CT and commandable breaker at the transformer hut.....(per recommendation 4 of the presentation)

Residential loads are presenting themselves as more industrial in nature more and more now.

Upsize neutral now....

Learnt something today. Thanks Naha.

Now I can spec a neutral CT and commandable circuit breaker for some of my installations, or instal bigger neutrals. Margin just got a bit better.

Also be considering the acquisition of some true RMS instruments.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#9

Re: Sizing Neutrals Single Phase Distribution

03/28/2015 5:20 AM

Wal, gr8 link thank you Sir!

BTW both the US and British codes mention sizing neutrals due to actual loads and heating. This comes right when i was getting comfortable with the idea of downsizing neutrals, now thats obviously not a good idea.

Everyone should read Wal's link carefully and think about it.

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: Sizing Neutrals Single Phase Distribution

03/28/2015 5:44 AM

Thanks for the acknowledgement 1c.

A day doesn't pass where I don't learn something new.

APFCs and Harmonic filter installations could be a more common place installation requirement too...like I said, good for the margin.

But mate, "Sir!"??? Knighthoods are for gay minstrels and jesters....

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Jul 2011
Posts: 34
Good Answers: 1
#11
In reply to #9

Re: Sizing Neutrals Single Phase Distribution

03/29/2015 2:18 AM

Good article. It does not however suggest that increasing neutral cable size is the best solution since the transformer still has to deal with the adverse effects of the harmonics and so has to be derated. It seems to favour other approaches for dealing with harmonics.

Considering that this article was written about 14 years ago, it is also good to see what advances have been made and are being incorporated into non-linear loads. This article from GE discusses the solutions they provide alongside their VFD's.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#12

Re: Sizing Neutrals Single Phase Distribution

03/30/2015 1:44 AM

the article suggests k-factor rated transformers over de-rating regular transformers. but its also suggests derating cables or upsizing neutrals. IEEE 519 table 10.3 requires (suggests ???) THD to be kept to 5%. Here

http://www.mirusinternational.com/downloads/Interpreting-IEEE-Std-519-and-Meeting-Harmonic-Limits-VFDs-PCIC-2003-15.pdf

we have an example of a THD which uses 182 amp/3p at 60hz,
using 233a/3p RMS because of its harmonics = (51 amps harmonics/182 amp fundamental) = 28% THD

__________________
BSEE but always learning
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers: