I think that I have to use detuned reactors when the frequency of some harmonic current present in the network not only match but also is very close to the frequency resonance of the system.
We have an installation where we have variable speed drives driving several motors, with a 2000 kVA power distribution transformer with %Z = 5,94, and we pretend to install a 315 kVAR capacitor bank for power factor correction.
Using the expression h(resonance frequency order)=square root (kVA trasnf / kVAR cap bank * Z%) we obtain a value approximated to 10,6 (636 Hz).
The harmonic current frequencies with major presence are the 5th and 7th (300 Hz and 420 Hz respectively).
My question is: Must we use detuned reactors in this particular case?
Gustavo