I Have A Doubt About Using Detuned Reactors With Capacitors Banks

03/31/2015 9:41 AM

I think that I have to use detuned reactors when the frequency of some harmonic current present in the network not only match but also is very close to the frequency resonance of the system.

We have an installation where we have variable speed drives driving several motors, with a 2000 kVA power distribution transformer with %Z = 5,94, and we pretend to install a 315 kVAR capacitor bank for power factor correction.

Using the expression h(resonance frequency order)=square root (kVA trasnf / kVAR cap bank * Z%) we obtain a value approximated to 10,6 (636 Hz).

The harmonic current frequencies with major presence are the 5th and 7th (300 Hz and 420 Hz respectively).

My question is: Must we use detuned reactors in this particular case?

Gustavo

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: I've a doubt about to using detuned reactors with capacitors banks

03/31/2015 10:03 AM

Power Factor correction utilizing capacitors and inductors will affect system induced harmonics but does not fully address your issues.

I would suggest you first identify the source of all harmonics then eliminate them by installing tuned harmonic filters wherever necessary and as local to the culprit VFD(s) as possible.

Once you eliminate the harmonics it should be relatively easy to address any PF correction needed to the supply power.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: I've a doubt about to using detuned reactors with capacitors banks

03/31/2015 11:09 AM

I'd have a go at eliminating those naughty harmonics at source rather than at the downstream equipment, Mildred, then I'm funny that way.

__________________
Good moaning!
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: I've a doubt about to using detuned reactors with capacitors banks

03/31/2015 12:37 PM

This is a very interesting question in that methods of %Z are being used. But I am confused by the term "detuned reactor" since line reactors are simply inductive chokes in series with your VFD (variable frequency drive).

I suppose there are several methods by which the analysis could be performed, but the ratings I've seen in the catalogs have been based on a particular sized load with the choice of 3% or 5% reactance. All of this assumes that the fundamental frequency is 50 or 60 Hz at which frequency, the impedance will be smallest. At multiples of the fundamental, the impedance then increases proportionally so that harmonic current is suppressed more and more with higher octaves, right at the load.

If these harmonics are not suppressed, the capacitor bank may experience higher voltages than they are rated for by having the current in phase with and adding to the fundamental current. In some cases, the capacitors may ignite and burn up. I've seen this where I work. Consequently, I have been adding line reactors where there were none installed, and it seems to be improving (reducing) the harmonic content.

I'd like to know more about this myself. It feels like circular reasoning when trying to come to terms with the details of a particular solution. So far, line reactors seems to be the least costly of the options for treatment.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: I've a doubt about to using detuned reactors with capacitors banks

03/31/2015 4:58 PM

A

passive harmonic Filter" for VFDs is essentially exactly what you are describing doing on your own, it is a set of reactors and capacitors with RC snubbers that are tuned to the 5th and 7th harmonics, which make up the majority (but not all) of the THD coming from a 6 pulse inverter drive.

The problem with PHF systems is that they work today, then if something changes, they no longer work. I never recommend them for anything but the most rock solidly unchanging systems. In addition, the cost for PHFs tends to make them uncomfortably expensive once you get above 100kW drives. You never say what size drives you have or how many.

Lately I have been using Active Harmonic Filters instead, especially if there are multiple VFDs, and especially if they are not all running at the same time. The AHFs will track the harmonics and inject corrective current AS NEEDED into the system. As a general rule, an AHF can actively trach and correct your ITHD to less than 4%. The best I have ever seen with a PHF system is correcting to 7% ITHD.

If you have just one or two large VFDs, you might also consider going to an 18 pulse front end. But if the VFDs already exist, that can be challenging.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2015
Posts: 11
#5
In reply to #4

Re: I've a doubt about to using detuned reactors with capacitors banks

04/23/2015 11:33 PM

12 pulse front ends are good enough to meet the usual specifications and don't have the problems 18 pulse do with regard to unbalanced input line voltage. if you can build a 12 pulse system by adding a single transformer and 6 more diodes to your existing VFDs then it will be significantly cheaper compared to an 18 pulse, which will require a transformer rated to 1.1 kva requirement rather than the 0.57 pu required for a 12pulse configuration (augmenting the straight through connection to the line) The tapped inductor required should not be a significant cost either.

far as i know most 18 pulse configurations run the three rectifiers in series to avoid using a tapped inductor, so you have to buy a new transformer.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); johansense (1); JRaef (1); NotUrOrdinaryJoe (1); SHOCKHISCAN (1)