Flow Control

07/11/2007 6:57 PM

Can anyone assist me on how I can achieve flow control of Argon gas on a range of 1 to 80Nm3/h. The range is too wide to accurately control at either extreme end. I was thinking of using a two stage control for low range and high range.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: May 2007
Location: Australia
Posts: 27
#1

Re: Flow Control

07/11/2007 11:55 PM

Hi

Since your question is very general the answer to it also can't be very specific unless more information provided.

First was wondering what N stands for beside your flow rate unit?

Second,your flow rate range as you have indicated is very wide, so the next problem encountering is the flow velocity and pipe diameter and friction losses.

Usually based on the allowable friction loss for different gases the pipe size vary based on differential flow rate( maximum and minimum).

so based on your end user required flow rate and the distance, as you have also mentioned provide required number of controller for each branch.

Good luck

__________________
Never laugh at anyone's dream. People who don't have dreams don't have much.
Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#2

Re: Flow Control

07/12/2007 5:28 AM

If you want to measure the normalised volume of a gas I would suggest a mass flow meter as being the most suitable...

For the range of 1300litres/min down to 17 litres/min (80 m^3/hr to 1m^3/hr) there are several mass flowmeters which can easily cope with that turndown.

All that's needed is the accuracy or reading and loads of other effects to be able to select the right transducer for your application.

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Reply
Active Contributor

Join Date: Dec 2006
Location: Randburg, South Africa
Posts: 10
#3

Re: Flow Control

07/13/2007 2:33 AM

One valve cannot work because of constant valve CV. Therefore make a split range final element where different valves are used each with the correct CV over a specific range. Adjust the controller to give the correct control force signal to each of the valves by splitting the control force signal (say 4 - 20mA) into (say) three ranges. Each valve is then sensitive to the appropriate range signal. Have used this succesfully.

__________________
Wessel Pieters
Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4

Re: Flow Control

07/13/2007 4:01 AM

To design control system also need to know ΔP across valve at both flows. Usually valve ΔP is higher at lower flow - reduced pipe friction, compressor running up curve, etc. Full range of Kv (or Cv in US) then given by min flow/max ΔP vs max flow/min ΔP, and is likely to be even greater than 1:80.

As you say, can't do this on one valve. I'd suggest 2 in parallel. If actual Kv range = say 100, design each for √100 = 10. Valve A for 1:10, valve B for 10:100. Control on A for low flow, with B closed. When A fully open, control on B up to max flow. Kv range 1:10 is well within range of a control valve.

Cheers....Codey

__________________
Give masochists a fair crack of the whip
Reply
Anonymous Poster
#5

Re: Flow Control

07/13/2007 11:32 AM

ARGON ===> REGULATOR ===> dP Flow Sensor ===> Valve ===> Rotameter

This set-up works well across a fairly good range if you size your orifice plate to cover the dP flow in your needed range. Bore sizes are available down to a very small diameter. Calibration and zero trim adjustments are quite simple to keep your process readings accurate. The rotameter will suit flow loops where the dynamics of the system are minimal, (ie SP adjustment is fairly uncommon). An alternative for dynamic control would be a dP secondary loop to control the flow in the primary loop in a cascade type set-up. Sizing will be crucial here again, and depending on the dynamics, you may be having to watch for stiction depending on pipe and supply distances as well as your control valve travel as you'll start to notice stem wear and slop over time. Another issue is you'll need more instrumentation. This can be done within a decent budget...Good Luck.

Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#7
In reply to #5

Re: Flow Control

07/13/2007 12:29 PM

The flow rate has a turn down ration of 80 to 1....

You will be very lucky to get a turndown ration of 10 to 1 with an orifice plate and rotameter.

As the gas is reasonably pure i.e. Argon, a mass flowmeter would be ideal.

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Reply
Member

Join Date: Jul 2007
Posts: 8
#6

Re: Flow Control

07/13/2007 12:26 PM

I don't know if this will you, all you need is a regulator that can control the flow. You can surf on the web for more info.

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#8

Re: Flow Control

07/16/2007 4:15 AM

Just another comment - some of the contributors appear to be answering a question that wasn't asked, ie about flow measurement, whereas question was about flow control. The flow controller could respond to various inputs, not necessarily a flow signal.

If you do need to measure the flow, as Electroman said, 1:80 can be done with a mass flowmeter. Spec sheet I have from FCI (1999 but if anything there'll be improvements since then) says 100:1 standard, 250:1 option. But if you use my suggestion of 2 control valves in parallel you could put a flowmeter in each leg, with lower turndown (and add the readings, naturally)

Cheers.....Codey

__________________
Give masochists a fair crack of the whip
Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers: