Tripping 6.6 kV Motors on NPS Protection

04/16/2015 2:49 AM

pl. clarify - there was a system disturbance in the 400 kV system, which has led to tripping of 210 mw generator on Class B protection - Negative Phase Seq Stg-2 and subsequently, the numerical relays of HT motors have acted on NPS protection and tripped HT motors...Why pl. Clarify..?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Tripping 6.6 kV Motors on NPS Protection

04/16/2015 11:47 AM

The relays acted properly. You have to look at what causes a NPS relay to operate; i.e., they detect high levels of Negative Sequence voltages/currents, depending upon the exact type.

You didn't say what the nature of the system disturbance was, but assuming it was a single line to ground fault then the remaining two phases essentially continued to power the system as a severely unbalanced single/three phase system (depending upon the transformations between the fault and the relaying).

This in turn caused negative sequence currents to flow far in excess of the 5% trip level that the machines' protective relays may be set for. Given the fact that it reached as deep as the generator the fault must have persisted for quite a long time, long after the HT motors tripped.

Did something take out a tower or get tangled in the conductors?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)