Anonymous Poster #1

Bus Bar Rating

04/20/2015 10:45 AM

Hi,

I have a main distribution board (MDB) with a Main circuit breaker rating of 160 Amps. How much should be the rating of the MDB's bus bar?

Is it acceptable to consider it always as the next higher rating of the Main circuit breaker? Say 200Amps in this case.

Thank you a lot.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Bus bar rating

04/20/2015 10:57 AM

Busbar design is, like cable sizing, one of CR4's most popular topics. Enter the appropriate words into the Search This Forum box on the right, and all sorts of previously-enjoyed information will be revealed. Far better, one hopes, than this thread becoming labelled a duplicate and closed?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Bus bar rating

04/20/2015 11:19 AM

Thanks PWSlack.

However the replies are contradicting. Some may agree that the circuit breaker and bus bar ratings are the same; while others state that the rating of the bus bar should be greater than the circuit breaker one. What would you say??

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Bus bar rating

04/20/2015 11:23 AM

The circuit breaker has to protect the cabling and busbars downstream. Otherwise there is no point in having it.

British Standard 7671 says this, rather than any individual. These things are not, after all, matters of opinion!

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Anonymous Poster #1
#6
In reply to #3

Re: Bus bar rating

04/20/2015 11:40 AM

Thanks. In this case it should be 200Amps.

Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#13
In reply to #6

Re: Bus bar rating

04/21/2015 9:09 AM

The choice is up to you. Are you ever going to need extra power distrubuted?? You can oversize the buss now while you are doing the installation in that case. My opinion would be to oversize to what you feel your future load may be. A lot of the cost will be in the installation and upsizing by 40 amps(or more) on the buss should be relatively inexpensive at the start as you are basically looking at conductor size only. Then if you need more power to the buss, changing out the main(and possibly feed lines to the buss if you don't do it start with) will be all you have to do.

Always try to look into the future to see what is going to be required for power and distribution of same. A few extra $ up front now can save a lot of $$$$ down the road.

__________________
Never stop learning
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Bus bar rating

04/20/2015 11:24 AM

My impression is you try to guess the possible bus bar rated current according to the existing circuit breaker.

"To guess" it is not a technical way to appreciate this.

You have to calculate the bus bar steady state maximum permissible current according to losses and cooling process and to check the dynamic stability to short-circuit. You may state at first the maximum available current -in both cases-and to follow a suitable calculation mode-IEC 60909 , IEC 60865, IEC 60694 and so on.

The circuit breaker will protect the entire installation-cables mainly.

__________________
Julius
Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5

Re: Bus bar rating

04/20/2015 11:32 AM

Most panels are marked what the maximum panel rating is.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7

Re: Bus bar rating

04/20/2015 1:09 PM

The bus bar feeding the 160 amp MCB should be rated for a minimum of 160 amp.

It is not acceptable nor is it safe to assume the next higher rating of any MCB.

The MDB is designed for a maximum rated amperage and voltage value that cannot be exceeded.

There should be an OEM tag located somewhere on the board/panel that gives the voltage rating, the maximum bus current rating, and the maximum allowable current rating of the Main Circuit Breaker permitted to be installed.

If this information is not available on/in the MDB or is not ledgible, contact the manufacturer for clarification before proceeding.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Bus Bar Rating

04/20/2015 3:42 PM

Having a breaker with a 160A rating indicates that you are not in North America, so I can't address rules applicable to your location, but in general, I have seen they tend to be the same or similar.

Here, a basic standard circuit breaker is often referred to as being "80% rated", meaning it can only be loaded to 80% of it's value continuously (defined as 3 hours or more). The main reason for this is because our rules on sizing conductors call for the conductor to be sized for 125% of the continuous load, and 80% is the inverse expression of 125%. So in theory if you used CONDUCTORS rated for 160A, you could not use a 200A circuit breaker because even though that is can be loaded to 160A, your CONDUCTORS cannot be loaded to more than 128A.

But bus bar is sized and rated for 100% of the continuous load so you COULD feed bus bar sized for a 160A load with a 160A breaker. But because the breaker mfrs know that most breakers are only going to be able to be loaded to 80%, they now design them that way. So if you WANT to get 160A continuous current through it, you would buy a 200A standard breaker (200A x 80% = 160A), or a 160A breaker that carries a "100% rated" listing.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#9

Re: Bus Bar Rating

04/20/2015 4:17 PM

While the information presented by JRaef is perhaps accurate for a US based installation under the NEC, it is interesting to note that the Canadian perspective is a little different in subtle but important ways (we do not require 125% ampacity on conductors feeding continuous loads).

What this does show is that... there are no tried and true answers to allot of these questions. You need to know what the codes and standards are in place in the jurisdiction that the equipment ie meant for and then follow them.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Good Answer (Score 2)
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#10

Re: Bus Bar Rating

04/20/2015 4:22 PM

Who is installing this electrical equipment?

  1. You are posting anonymously!
  2. You do not seem capable of installing this equipment!
  3. Hire a competent licensed electrician!

You are endangering yourself and any other person that would be in that structure!

If you install it and there is a fire or electrical shock and someone dies, you will be held criminally liable and the insurer will most likely deny any damage claim!

That means they will sue you if you're not in prison or they may sue your estate which means your family will bear the burden of your inexperience!

  • Hire a competent licensed electrician!
  • Hire a competent licensed electrician!
  • Hire a competent licensed electrician!
__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: Bus Bar Rating

04/20/2015 11:01 PM

Calculate the SC level at the incoming CB. Busbar should withstand,without melting, any value current for which CB provide protection.

__________________
pnaban
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#12

Re: Bus Bar Rating

04/21/2015 2:57 AM

Which electrical code are you working with, Mildred?

__________________
Good moaning!
Reply
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Anonymous Poster (2); Crabtree (1); JRaef (1); Kevin LaPaire (1); North of 60 (1); Original_Macgyver (1); ozzb (1); pnaban (1); PWSlack (2); SHOCKHISCAN (1)