test standards required

07/13/2007 1:31 AM

what is the stndard test data for

1) EARTHING TEST

2) High VOLTAGE insulation test.

The above should be for units which are approx 25KW power consumption working on 3ph+ N +Earth.

I need to have the saftey guidlines with required data.

Pls advise ASAP

Regards

Rajesh

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#1

Re: test standards required

07/13/2007 7:21 AM

Refer some IS or IEC standards and get all the information you require.

__________________
BNDas
Reply
Active Contributor

Join Date: May 2007
Posts: 10
#2

Re: test standards required

07/14/2007 7:17 AM

For Earthing test:

For all electrical installations: less than 5 Ohm ( in rocky areas allowable upto 7 Ohm)

For Lightning conductor:the combined value of the earthing system shall be less than 10 M.Ohm

For High voltage test:( should withstand the RMS ac voltage applied across frame & live parts for 1 minute)

For fractional HP motors of rate voltage <50V - 500V ; above 50V upto 250V - 1000V

For motors 1 HP to 3 HP - 1000V + 2*rated voltage

For motors above 3 HP - 1000V + 2*rated voltage

( subjected to maximum of 2000V)