Mass flow measurement-hot air

07/13/2007 1:44 AM

hi,

i am to measure mass flow of hot air (725 deg C). the mass is in the range of 25000 to 35000 kg/h. The hot air i must mention is dust laden (approx 0.2 to 0.4%). And the accuracy of the measurement can be +/- 2%. Can you suggest me the right type of instrument / method?

thnx in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Mass flow measurement-hot air

07/13/2007 9:06 AM

Mr Satish

This type of measurement can be done through Dantec Instruments ( Hotwire Anemometer ). For more details please contact Dantec people.

MOHD. SAEED KHAN

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member Hobbies - Musician - New Member

Join Date: Jun 2006
Location: Wilmington, NC
Posts: 167
Good Answers: 4
#2

Re: Mass flow measurement-hot air

07/13/2007 10:51 AM

Hi Satish,

Hot-wire anemometry is good for dust-laden environments, but will only give you a velocity at the point where it is measured. To sufficiently obtain an accurate average velocity, many such measurements would be needed to be taken simultaneously with an array of hot-wire sensors on the plane of the cross-section of the duct. This average velocity is then used (along with sensed temperature and pressure) to obtain the mass flow rate.

Are you sure that the temp in the duct is 725ºC and not 725ºF? Being this hot would raise some problems even with hot-wire anemometry.

Is there another, cooler section where the measurement could be taken?

Your best bet would probably be an orifice plate. The pressure drop in the duct caused by the orifice plate is used to obtain an average velocity. If you also measure temperature and duct pressure, these can be combined to obtain the mass-flow rate. There will also be some calibration involved. This would be the best method considering the temperature and particulate content in the duct. What I can't tell you is what the accuracy would be. It is quite likely that, with proper calibration and accurate duct temperature and pressure measurements, you would be within the ±2%.

I have done work on coal-fired energy plant ducts using patented pitot devices (http://www.easterninstruments.com) but the temp was only 500ºF max.

Hope this helps.

Mike

__________________
"Blessed is the man who, having nothing to say, abstains from giving us wordy evidence of the fact." George Eliot [Mary Ann Evans] (1819-1880)
Register to Reply
Active Contributor

Join Date: Nov 2006
Location: Mumbai, India
Posts: 17
#3
In reply to #2

Re: Mass flow measurement-hot air

07/14/2007 2:34 AM

hi mike...thnx. the hot air generator is a coal fired fbc. and the dust laden hot air is at 725Deg C and not F. we tried anemometry..but the temp is a problem. with the orifice plate..the pressure drop creates a problem downstream where the air is supplied. we are now convinced ..almost...tht the pitot tube is the best way...will refer the site u mention...thnx a lot.

Register to Reply
Anonymous Poster
#4

Re: Mass flow measurement-hot air

07/14/2007 4:00 AM

Dear Mr. Satish ,

You can use Orifice Plate for such Flow measurement , which we manufacture. The following data are required to see suitability & estimate price

Pipe/ Duct OD & ID , Pipe/Duct Material , Operating Temperature & Pressure ,

Flow Range.

Regards

Register to Reply
Power-User

Join Date: May 2006
Posts: 142
Good Answers: 3
#5

Re: Mass flow measurement-hot air

07/15/2007 12:30 PM

can you measure at the inlet before the addition of heat and dust? if so differential pressure transmitter to ddc for variable calculation or differential pieto readings at magnahelic guage a simple math from there.

Register to Reply
Active Contributor

Join Date: Nov 2006
Location: Mumbai, India
Posts: 17
#6
In reply to #5

Re: Mass flow measurement-hot air

07/16/2007 1:34 AM

hi conwaymech..& guest,

thnx..input is from 3 diffeerent sources and one being not measurable as also the largest. so for now i think i am going ahead with the pitot tube arrangement..will get back with the results. Mr guest..can u give me ur email pl? i wud like to mail u the details.

thnx..Satish

Register to Reply
Power-User

Join Date: May 2006
Posts: 142
Good Answers: 3
#7
In reply to #6

Re: Mass flow measurement-hot air

07/16/2007 8:25 AM

CONWAYMECH@YAHOO.COM

Register to Reply
Active Contributor

Join Date: Nov 2006
Location: Mumbai, India
Posts: 17
#8

Re: Mass flow measurement-hot air

12/05/2007 4:41 AM

hi all,

we tried the pitot tube with a digital manometer and its working just fine. thanx a lot for all the inputs!

satish

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member Hobbies - Musician - New Member

Join Date: Jun 2006
Location: Wilmington, NC
Posts: 167
Good Answers: 4
#9
In reply to #8

Re: Mass flow measurement-hot air

12/05/2007 8:16 AM

Hi Satish,

Thanks for letting us know how things went.

Mike

__________________
"Blessed is the man who, having nothing to say, abstains from giving us wordy evidence of the fact." George Eliot [Mary Ann Evans] (1819-1880)
Register to Reply