Dear All,
We are having GEMSTART 5 relay with Toroidal CBCT (10A/0.0167mA) for LV Motor Earth Fault Protection in LV Switchboard (415V)
Setting in GEMSTART 5 as follows ;
Earth Fault Method : EF Input
Earth Fault CT Primary Rating :
Range 1.0 - 10.00 A
Value 10.00A
EF Protection Speed 1
Ignore Earth Fault At Start For 0.4 s
Remote Earth Fault Resets Enabled No
Earth Fault Trip Current Range 1.0 - 10.00 A
Earth Fault Trip Current Value 2.00 A
EF Trip Current During Startup 2.00 A
Delay To Detect Earth Fault 0.0 s
(Additional) Delay To Trip 0.0 s
Once we inject 2.2A in cable through CBCT via secondary injection we are getting EF tripping time of 300-400ms on instantaneous setting which is should be around 50ms
Anyone having faced same problem with Gemstart 5 & toroidal CBCT??
Any solution to above problem???
Regards,
T.D.
Good Answers: 445
Re: GEMSTART 5 with Toroidal CBCT : Long Earth Fault Tripping Time on Instantaneous
05/04/2015 1:02 PM
Not quite sure which model you have, so I don't know what other inputs you have besides the CBCT, so I'm assuming that you bench testing the relay by powering it up, letting it stabilize, then putting a 2.2A step into it.
Let's consider what the relay logic sees; it goes from "no input" to 2.2A instantly, then waits 400msec to issue a trip.If so then it's operating properly by assuming that it's a cold start and the delay is to let any transients wash out. You think it should trip instantaneously because you injected a current above the threshold, the only problem is that "instantaneous" is missing the condition "after the motor has been running for awhile".
Change your test setup to first put some voltages on the input to tell the relay "the motor's been running for awhile" or inject a much lower current then increase it to 2.2A and see how long it takes to trip when you do the increase.
05/04/2015 11:41 PM
I appreciate your response
We have GEMSTART 5.4 Relay for Motor Protection
For EF we only have Toroidal CBCT connected to 22 & 23 Terminal of GEMSTART
Test Condition as Follows:
- 3 phase supply cable connected to Gemstart Module passing through Toroidal CBCT
- We inject 2A balance three phase current using secondary injection kit
- Then we increase / inject 2.2A current in one phase in order to create unbalance current to be detected by Toroidal CBCT
- We are getting 300-400ms EF tripping time which is not instantaneous
Requesting your further advice
Regards,
T.D.
Good Answers: 102
05/05/2015 12:39 AM
It seems a little more than coincidental that the trip delay is close to the ignore fault at start value.
Have you tried altering the Ignore Earth Fault at start value to say 0 and retesting?
05/05/2015 1:08 AM
Yes we have also tried making Ignore Earth Fault at start value = 0, But EF tripping time is same no change....
Good Answers: 102
05/05/2015 3:27 AM
Should trip if you drop a phase too.
Have you tried that instead of injecting additional current into 1 phase?
05/05/2015 1:45 PM
I'd pick up the phone and talk it through with the manufacturer if it were me. Then, I'm funny that way.
Good moaning!
05/06/2015 12:31 AM
These all common sense things u mentioned allready done.
I have already taken up with manufacturer and they confirmed it is not possible for GEMSTART to trip on EF in less than 200- to 300ms when current of 2.2A applied on setting of 2A EF setting
They also confirmed "if the current value is more than 100% ( EX: In= 2A; I tripping= 4 A ) the time trip shall be under 100ms"
However, as an electrical engineer, product supplied by manufacturer stating Instantaneous EF protection feature then it should perform the desire function. 200 to 300ms trip time cannot be treated as instantaneous isn't it???
I just wanted to find out if somebody have faced similar problem with GEMSTART or there is some issue with respect to Toroidal CBCT used for EF detection with GEMSTART
Regards,
T.D.