Dear All,
We are having GEMSTART 5 relay with Toroidal CBCT (10A/0.0167mA) for LV Motor Earth Fault Protection in LV Switchboard (415V)
Setting in GEMSTART 5 as follows ;
Earth Fault Method : EF Input
Earth Fault CT Primary Rating :
Range 1.0 - 10.00 A
Value 10.00A
EF Protection Speed 1
Ignore Earth Fault At Start For 0.4 s
Remote Earth Fault Resets Enabled No
Earth Fault Trip Current Range 1.0 - 10.00 A
Earth Fault Trip Current Value 2.00 A
EF Trip Current During Startup 2.00 A
Delay To Detect Earth Fault 0.0 s
(Additional) Delay To Trip 0.0 s
Once we inject 2.2A in cable through CBCT via secondary injection we are getting EF tripping time of 300-400ms on instantaneous setting which is should be around 50ms
Anyone having faced same problem with Gemstart 5 & toroidal CBCT??
Any solution to above problem???
Regards,
T.D.