can any one help me to know the accuracy class in transformer, motor,circuit breaker etc. what is it means 1/5p20.please explain clearly as i eager to know this .
Anonymous Poster
Re: Accuracy Class
07/13/2007 11:34 PM
Presumably you refer to a current transformer. "5" deonotes the composite error, "P" the class [i.e. protection desiganation & "20" the accuracy limit factor. For more info refer to the Standard IEC 185 or later editions.
Greg Lynch
Anonymous Poster
Re: Accuracy Class
07/14/2007 1:19 AM
IEC 185 is withdrawn. refer IEC 60044 Part1 for current transformers
Anonymous Poster
Re: Accuracy Class
07/15/2007 6:45 AM
5p20 is denoting class of current transformer. which is using for power system protection such as over current protection,earthfault protection and distance protection.Initial letter 5 shows that accuracy class of the current transformar.This means 5% error allowed at the rate of multiple rated current(here 20 times-last letter),if the connected burden equals to rated burden. P is denoting protection.