HT motor

07/13/2007 10:22 PM

Why HT motors are star-connected?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: HT motor

07/13/2007 11:43 PM

Why HT motors are star-connected?

It is highly unlikely that a HT motor would ever be started by the star/delta method. By star connecting the Volts/Turn is reduced to the minimum.

Greg Lynch

Register to Reply
Active Contributor

Join Date: Jul 2007
Location: INDIA
Posts: 14
#2
In reply to #1

Re: HT motor

07/14/2007 2:55 AM

Hi,

I`ve got 24 Nos.HT motor which all are star connected reasonbeing insulation level as we aware in star mode phase voltage become V (line)/1.732 mean we have saved insulation for that system.Suppose we choose delta connected HT motor we will have to increase insulation level.It will bw sheer wastage of money beside it size of motor become too large.

Good luck

tadagids

Register to Reply
Member

Join Date: Jul 2007
Posts: 5
#3
In reply to #2

Re: HT motor

07/14/2007 4:30 AM

Thanks for reply,

What about torque? Delta connected motors have more torque.

Register to Reply
Active Contributor

Join Date: Jul 2007
Location: INDIA
Posts: 14
#4
In reply to #3

Re: HT motor

07/14/2007 4:48 AM

Raja,

Good question.

We know about torque but economy also prime factor for an engineer .If you ask for torque then go for Slip Ring Motor so that one can insert resistance in its rotor circuit & can increase torque accordingly .Check torque formula for induction motor.

Good luck

tadagids

Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#5
In reply to #4

Re: HT motor

07/15/2007 11:19 PM

Good reply on the both cases.

__________________
Subramanyam
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #3

Re: HT motor

07/16/2007 4:39 AM

It is the mechanical load that presents the torque/speed characterisitics to the motor, and motors and their starting arrangements must be selected with this as a primary consideration.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7
In reply to #6

Re: HT motor

07/20/2007 3:28 AM

In HT motor by connecting in Star u have only one weak spot. Connecting in Delta would mean three joints. Though voltage will be rated by 1.732 full insulation is used and not graded insulation as done in case of transformer because the HT voltage levels used max are 11KV (Though some 33KV motors Have been reported to be in use.)so saving in insulation will not result in cost reduction.Torque has nothing to do with connection.Torque is KW*K /speed or RPM.Type of connection won't make any difference.The reason they are always in Star is no advantage is gained by using delta,On the other hand weak spots are more.Secondly a neutral point helps in Protection.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 7 comments