O.C. Test of Transformers

05/29/2015 4:03 AM

So in the OC test of a transformer, why is it preferred to keep the H.V side open? And why do we supply the L.V side with rated voltage? it shouldn't matter, because the OC test provides us with the core losses which are constant at any load.

Register to Reply
Pathfinder Tags: tests transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#1

Re: O.C. Test of Transformers

05/29/2015 5:08 AM

I don't think it really matters: I suspect that it's normally easier to find a low voltage test source.

The "NO-LOAD LOSS AND EXCITING CURRENT TESTS" in this page says

"rated voltage is applied to either the high voltage or low voltage side while the other side remains open circuit."

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#2

Re: O.C. Test of Transformers

05/29/2015 12:26 PM

This OC????

HV?

LV?

Good acronyms. What do they have to do with a generator?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: O.C. Test of Transformers

05/29/2015 1:21 PM

What do you think would happen to the transformer if you short the HV side rather then leaving it open circuited, and then apply rated voltage to the LV? Maybe some smoke would come out of the transformer or the shorting cable. Or your LV source would experience an unhappy event...

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: O.C. Test of Transformers

05/29/2015 5:21 PM

OC? Over-Current Testing?

If Over-Current testing; Because it could be dangerous to personnel and harmful to the transformer as well as anything/everything attached to the high voltage terminals should there be a winding insulation failure.

If you were to short the HV terminals the xfmr windings might be damaged before the test set trips.

Applying rated voltage to the LV side is a true, accurate method of testing the windings turn-to-turn ratio and the insulation condition.

Is the transformer new, first-time-in-service or an in-service transformer?

Acceptance test? Or preventative-maintenance testing?

It is important that the transformer OEM is contacted and then follow their recommendations for all testing.

Good luck and stay safe!

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Participant

Join Date: May 2015
Posts: 1
#5
In reply to #4

Re: O.C. Test of Transformers

05/30/2015 12:04 AM

I am from a company called A&D Power in South Africa.

Short circuiting the HV side of a TX while applying rated voltage on the LV side can result in the TX being damaged and workers getting hurt.

When we test a HV / LV TX we normally do a insulation resistance test with a megger on double the working voltage before we supply voltage to the TX. Then we follow with supplying the LV side with rated voltage and testing the voltage on the HV side to ensure all coils are in working order. If all that readings are within spec then we go ahead by doing a final test, we short circuit the LV side and then supply the HV side with rated LV voltage,then we tong test the tails on the LV side to ensure the same current is flowing. This is the only way that we have found are sufficient testing without having expensive testing equipment needed.

I hope this helps.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7
In reply to #5

Re: O.C. Test of Transformers

05/30/2015 7:08 AM

Very tidy explanation of your method.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: O.C. Test of Transformers

05/30/2015 12:46 AM

You leave one side open and apply power to the other because your goal is to get the "No-load" losses. You would short circuit one side and apply a reduced voltage (equal to the voltage required to circulate rated current) on the other to get the rated full load losses and the impedance.

Magic smoke does not appear if this is done by qualified personnel, but it is useful for drying out a moisture laden transformer.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#8

Re: O.C. Test of Transformers

05/30/2015 7:10 AM

The reason for using the low voltage coil for the open circuit test is that is usually the coil closest to the core and the coupling is slightly better, especially in high voltage step down transformers. If the voltage is high enough you might have as much as 7 inches between windings on radial build which would mean more stray losses included in the open circuit test which would incorrectly add to the core loss measurement or open circuit test. If the LV winding is on the outside, and farther from the core, then the HV winding should be used. This is for core form transformers only, the analysis gets more complicated in shell form transformers.

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#9

Re: O.C. Test of Transformers

06/01/2015 5:42 AM

OC is conducted to measure no load losses and magnetizing current. For this you need watt meters, ammeters, voltmeters. If you apply input voltage from low voltage side, you will need all instruments suitable for low voltage, arrangement or set up is also required suitable for low voltage.Only voltmeter for measuring secondary voltage will be suitable for higher voltage. All this is safer and cheaper as compared to the same for high voltage side application. Theoretically speaking, there should be no difference whichever side you apply the voltage.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); Original_Macgyver (1); pcchatur (1); PeterT (1); Petrus Marais (1); RAMConsult (1); Randall (1); SHOCKHISCAN (1); Wal (1)