Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 8:08 AM

Dear sir,

recently we commissioned a unitrol 5000based static excitation system. Till date it hasn't shown any problem, but all of sudden avr started misbehaving like unable to build up voltage ang tripping on rotor earthfault. In further analysis we found out that a card snubber creating problem. Manufacturer suggested to isolate the card and run the system. How a card of ac protection is creating problem on dc side.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 12:19 PM

That is a question for the manufacturer!

CALL THEM!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Member

Join Date: May 2015
Posts: 5
#2
In reply to #1

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 12:57 PM

Manufacturer is on the way to unit, but the fault has been cleared as soon as snubber circuit isolated, its puzzling me.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #2

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/30/2015 9:50 AM

<...its puzzling...>

That situation will persist so long as there is reluctance to use the telephone. Take the risk!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#3

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 1:14 PM

With the unit being microprocessor controlled, any fault is going to cause the system to alarm and possibly shut down. The unit is a contiguous machine that will protect itself if there are any alarms.

What did the manufacturer say?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Member

Join Date: May 2015
Posts: 5
#4
In reply to #3

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 2:28 PM

I too was expecting an alarm from avr, but dint get any. Generator tripped on rotor earth fault and during analysis we found out a thyristor bank snubber card was showing insulation resistance very low hence we isolated this bank and synchronized the unit.

on consulting he replied fault reflection from ac side to dc side through thyristor.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#5

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 5:35 PM

For one thing the filter circuits including the snubber circuits on/in both AC & DC are capacitive-coupled to ground.

Any fault in the AC side is directly reflected in the reconstructed DC waveform especially when without properly operating filter systems.

A failed AC snubber circuit can allow "drag-over" and passing/transferring of AC waveforms into the DC excitation which will cause severe disruption of the excitation, erratic generator loading, and/or damage to the rotor windings.

Operating the generator without AC snubber protection will cause very noisy operation, distorted DC waveform(s) and loss of generation capacity and/or rotor or other component damage.

I would not attempt to run a generator of any size with any excitation system snubber circuit disconnected.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Member

Join Date: May 2015
Posts: 5
#6
In reply to #5

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 9:57 PM

What I mean I we have a bank redundancy in avr, so one bank completely isolated from the circuit and with the remaining banks full load is easily achievable, and so system synchronized. Regarding distortion I will agree with you as filters wil clear noises from circuit.in the established circuit I hope no need to have an earth other than capacitive coupling.

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/29/2015 10:18 PM

A 600 milli-watt generator? The generator on my Schwinn bicycle....

Don't mind me. I'm just being a linguistic as..... again.

One of the things I've noticed over the years I've worked with massively powerful systems is the diagnostics monitoring devices work very well as long as the system works within the designed parameters. Once something fails you hope that the diagnostic system is what actually failed. This can be quickly and easily repaired. More often than not the massive system failed and also took out some of the diagnostic system with it.

My point here is that until you find and fix the root cause of your problem suspect any and all telemetry readings from a failing machine.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #7

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/30/2015 3:29 AM

I agree entirely, in the 70's I worked for a large US computer company, that (correctly) designed all its equipment to test various parts as it "Boots".

The problem was, that if any part failed a test, the Boot-up procedure simply stopped and posted an error code, which had to be looked at in a manual.....not a problem you might say....but if the manual was not to hand........

I eventually made a suggestion, that took several years to implement for all the equipment we had, that it would be better to test the relevant voltages for the processor in some way to be within specs, before running the processor up fully, then test the other parts, posting a message in English on the console, sometimes in LED display, explaining firstly what area was being tested, the test that was running at each point and the results if an error was found.....but it would test everything without stopping....giving a list of erros at the end.

It was FAR easier to fault find/fix such machines after that.....though no actual studies were made of "Repair speed" as far as I remember.....

My personal take was that some of the less intelligent technical staff, could now fix machines!!

We usually only replaced PCBs anyway......not that difficult!! Only good old hardy DTL Logic, with external diodes, at that time. Also easily repaired if no PCB readily available.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#9

Re: Rotor Earthfault Analysis in 600mw Synchronous Generator

05/30/2015 7:17 AM

Welcome to the digital world of circuit protection. Errors in the protection circuits have no bearing on reality. This just makes troubleshooting that much more fun. Go with the manufacturers recommendations. While they could be wrong, you will still get your best answer there.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); Andy Germany (1); Original_Macgyver (2); praneeth.snr (3); PWSlack (1); redfred (1); SHOCKHISCAN (1)

Previous in Forum: O.C. Test of Transformers   Next in Forum: Does the Difference in Hz Affect the Performance of an Amplifier?

Advertisement