Two Winding Transformer

06/05/2015 1:25 AM

We have transformer PRI. Delta and secondary have two winding star & Delta. Problem is that we getting voltage of 52volts between neutral and ground. Transformer is used for vfd. What is the cause ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#1

Re: two winding transformer

06/05/2015 3:39 AM

Three winding transformer is used for supplying power to 12-pulse VFD.

The neutral-to-ground voltage you are measuring is due to the harmonics introduced by the VFD in to the upstream source. This is common with VFDs and the Technical manual should explain you more in detail.

Your neutral is probably unearthed and the insulation point of view, there shouldn't be any concern as the transformer winding neutral is rated to the same level as the winding line terminal ('uniformly insulated').

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2013
Location: Karnataka, India
Posts: 4
#2
In reply to #1

Re: two winding transformer

06/05/2015 4:00 AM

Right Sir,

But neutral is earthed, still getting voltage.

We have two transformers for PCC, both charged with bus coupler off. Both transformer neutral are earthed (both neutral connected together in PCC). Even one of transformer made off , still voltage persists.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: Two Winding Transformer

06/05/2015 10:49 AM

Do you have a circuit like this?

There are many ways to do this. Does it use 12, or 18 diodes?

More importantly, is your AC ground tied to your DC ground? If it is, then you may be shorting out certain diodes. In fact they are probably blown out. That is all it takes depending on where you pick ground on the AC side.

If you take a simple full wave bridge, tie one end of the secondary coil of a transformer to ground and then tie the DC + or - to ground, you are shouting out at least one diode. Once that diode is blown, you start to see unpleasant voltage shifts.

So, exactly what do you have?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Two Winding Transformer

06/06/2015 3:06 AM

In my opinion, the voltage between neutral and grounding it is measured far from transformer and close to VFD. So, the neutral in a three-phase cable could present a built-up voltage- if only one end is grounded- induction from the live conductors.

__________________
Julius
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#5

Re: Two Winding Transformer

06/08/2015 12:26 PM

It may also be due to the fact that you are using a digital voltmeter. They have such a high imput impedence that they can measure voltage in the air (so to speak)

If your neutral truely is connected to earth ground, it should be close to 0 ohms. If that is the case, then a reading of 52 volts would require hundreds if not thousands of amps.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6
In reply to #5

Re: Two Winding Transformer

06/09/2015 4:12 AM

In my opinion, it is not necessary. Let's say a 240 sqr.mm [500 MCM] single-core low voltage cables, laid in a single row R-S-T-N the neutral in 1000 ft. distance at 300 A/phase will get a built-up voltage of 54 V.

__________________
Julius
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); NotUrOrdinaryJoe (2); raghun (1); shinde (1)