Variable Frequency Drive for Asynchronous Motors

06/05/2015 7:23 AM

hello everyone,

if i have a motor which only draws less than 55% or half of its full load current, or driving a variable load, what are the losses in terms of the energy consumed ? and why is it necessary to use a variable frequency drive in such a case ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: variable frequency drive for asynchronous motors

06/05/2015 8:49 AM

Losses: Xc, Xl, hysteresis, core heating, mechanical resistance, and other dynamics introduced by the application.

A VFD allows regulation of speed and torque in a properly designed motor so that maximum efficiency of the motor can be attained throughout the motor RPM range used for the application.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Variable Frequency Drive for Asynchronous Motors

06/05/2015 3:58 PM

To expand on that, JUST putting a VFD on a motor does not save energy.

The only way to save energy is to reduce LOSSES in a system. A VFD saves energy only on CENTRIFUGAL (quadratic) loads, where the MACHINE needs less power as speed is reduced, such as some types of pumps and fans. Even then, the only savings in energy come from applications where you are using SOME OTHER form of flow control. Using the VFD to slow down the pump or fan and achieve flow control will reduce the LOSSES associated with that other form of flow control. Otherwise, the VFD, if you do NOT reduce the speed, will actually consume a little MORE energy.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#5
In reply to #2

Re: Variable Frequency Drive for Asynchronous Motors

06/05/2015 11:56 PM

GA

I wish more people understood that.

Less work = less power. This is the big efficiency saving.

The little bit of reduction that may be possible in magnetization energy can be lost in the drive itself - so no real net gain.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Variable Frequency Drive for Asynchronous Motors

06/05/2015 4:51 PM

There are fixed (no load) losses that occur because you are establishing the magnetic field around the stator and rotor, and variable (load) losses proportional to the mechanical work being performed by the motor caused by the additional current passing through the stator windings and the rotor bars.

It is not always necessary to use a VFD. Before you run out and buy one, you should examine everything about the motor, what it is driving, and how it interacts with the overall process that it is placed in. If your motor only draws 55% of its full load current, then it is only loaded to (approximately) 50% of its rated output.

From a simplistic viewpoint, it is twice as large as it needs to be; from a detailed viewpoint, you may find that it is oversized because it needs to start a high inertia load in a short period of time, maybe repeatedly, and the starting torque requirements of the load exceed that of a motor sized for the running torque.

If it is driving a variable load, then you need to examine how the speed to the shaft of the load is varied. If the load speed is a function of the process, then you need to examine how the speed change occurs. If it is through a variable speed mechanism, then the motor always runs at full speed and incurs additional mechanical losses in speed change.

The point is you must understand evrything about how, why, and when your motor/process consumes energy, long before you run off and buy the "latest and greatest" energy saving device.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Variable Frequency Drive for Asynchronous Motors

06/05/2015 5:38 PM

It occurs to me that the application may require varying torque values during normal operation such as initial starting or restarting under loaded conditions which most likely is the reason for an apparently oversized motor having been installed.

If you will identify how much and when maximum torque is needed throughout the cycle of operation it may be possible to purchase a motor with a specific torque curve which would allow a much smaller HP to be used thereby realizing some savings.

If you are able to do this the cost will be far less than purchasing a VFD, and a VFD rated motor, then suffering the cost of installation.

Depending on your location most motor OEM's provide on-site technical support to help you determine the best direction to go.

I would suggest you make the call to a reputable motor OEM and find out what the best options are before spending money on a "fix" that will not work.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#6

Re: Variable Frequency Drive for Asynchronous Motors

06/06/2015 11:10 AM

You really shouldn't put a VFD on a regular motor that is not designed for VFD.

The VFD motors have better insulation on the windings,and proper grounding of the

bearings to prevent eddy-current destruction of the bearings.

A regular motor will work,but will have a higher failure rate.

This issue is apart and aside from efficiency issues in your particular case.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#7
In reply to #6

Re: Variable Frequency Drive for Asynchronous Motors

06/24/2015 12:45 AM

With adequate filters it works OK on standard motors. But the cost may exceed a new motor, especially in small frame sizes.

These days most industrial motors in our part of the world have a vfd rating. Not cost effective to run two product lines.

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

GW (2); HiTekRedNek (1); JRaef (1); RAMConsult (1); SHOCKHISCAN (2)

Previous in Forum: Two Winding Transformer   Next in Forum: FCMA Starter

Advertisement