Earthing Cable Size Calculation

06/10/2015 5:29 AM

Dear all,

Please share ur advice for the calculation of earthing cable size for a panel board to earth grid connection. as i know the formulae per iec-61439 the earth bar in switchboard is provided with the formulae of A=sqrt of Isquad*t/k. The panel fault level is 25kA. my question is the contractor is provided earthing cable of size 70sq.mm to connect the earth bar to earth grid, where the panel vendor provided 50x10sq.mm busbars ie 500sq.mm. so wts the meaning of using of 50x10sqmm busbar to connect with 70sq.mm cable. if there is any other method to calculate the earthing cable size please share.

thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#1

Re: Earthing Cable Size Calculation

06/10/2015 6:31 AM

As you are probably aware, IEC61439 covers the manufacture and test of the switchboard, not the installation. For that you should refer to your local codes (e.g. UK - BS 7671). I am sure PWSlack will be on shortly to point that out :-)

It may be that the manufacturer of the switchboard has decided to standardise on only one size of earth bar, and had that tested, so he cannot now change to suit different installation conditions unless he re-tests. Bear in mind also that the calculation to which you refer only indicates the minimum size required to cope with the thermal effects - again sometimes busbars are uprated in order to manage the magnetic (mechanical) effects of a short circuit.

You could always try asking the manufacturer.

__________________
rogerggbr
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #1

Re: Earthing Cable Size Calculation

08/10/2023 5:09 AM

No need, now.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Earthing Cable Size Calculation

06/10/2015 2:53 PM

In order to calculate switchgear bus bar required cross section area you have to calculate the electromagnetic [electro-dynamic force withstand ] effect and also the thermal effect [thermal stability].

You may follow the IEC 60865-1and 2 Short-circuit currents -Calculation of effects.

In my opinion, in a case of rigid bar the dynamic effect could be the leading criteria.

On a cable thermal effect is the leading since the dynamic effect issue is easy to overcome here.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4
In reply to #3

Re: Earthing Cable Size Calculation

06/11/2015 3:37 AM

According to IEC 60865-1 -without considering vibration- if there is only one parallel bar of good resistance copper, in vertical position, fixed at 320 cm at both ends then 20kA [I"k] could be the maximum short-circuit current that this bar could withstand[approximately].

Thermal withstanding depends on duration[up to clearance of short-circuit].So, and 500 sqr.mm copper bar could withstand 70 kA within 1 sec[but not in this case].

__________________
Julius
Register to Reply
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#5
In reply to #4

Re: Earthing Cable Size Calculation

06/11/2015 3:47 AM

7anoter4:- 320cm is a long way - unlikely in a switchboard to be unsupported over such a length.

Earth bars are normally subjected to an asymetric test i.e. 60% of board fault level. Did you account for that?

__________________
rogerggbr
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7
In reply to #5

Re: Earthing Cable Size Calculation

06/11/2015 9:02 AM

Thank you rogerggbr! It was a wrong calculation-I did not close the loop-it has to be 90 cm.

However, it is only a rough estimation since I don't know all actual dimensions and material. My intention was to explain where are the limits-more or less.

No, I considered full short-circuit subtransient current[I"k] in order to calculate maximum force.

__________________
Julius
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Earthing Cable Size Calculation

06/11/2015 4:20 AM

What is the size of the incoming feeder?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#9
In reply to #6

Re: Earthing Cable Size Calculation

06/13/2015 9:39 AM

Its an MSB with 400A main incomer, the fault current only to be taken to account for the calculation of earthing conductor, here it is 25kA, only to confirm that symmetrical fault or only earth fault current to be considered. if it is e/f to consider i hope 70sq.mm is ok.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: Earthing Cable Size Calculation

06/14/2015 12:13 AM

If your incoming feeders are 70mm2 than that's fine.

but

70mm2 protected by a 400A breaker....cable seems on the small size unless it is very short. What will your service load be? Maybe a smaller breaker is required?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#8

Re: Earthing Cable Size Calculation

06/11/2015 10:50 PM

If you are working in India refer IS 3043 ( Indian Standards ) for all detailed information regarding Earthing. IS 3043 Clause 12.1 specifies the size of connecting cables for Earthing.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Earthing Cable Size Calculation

06/15/2015 1:40 AM

In my opinion, choosing the right grounding copper conductor cross-section area it is not a simple job. Let's start with the live conductors at first.

According to NEC Art. 240.4 Protection of Conductors. (B) Overcurrent Devices Rated 800 Amperes or Less.

"The next higher standard overcurrent device rating (above

the ampacity of the conductors being protected) shall be

permitted to be used, provided all of the following conditions

are met:

(1) The conductors being protected are not part of a branch

circuit supplying more than one receptacle for cord and-

plug-connected portable loads.

(2) The ampacity of the conductors does not correspond

with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).

(3) The next higher standard rating selected does not exceed

800 amperes."

So, 380 A rated conductor may be protected by 400 A MSB.

According to NEC 2014 Table 310.15(B)(16) 500 MCM copper 75oC withstand 380 A.

From Table 250.102(C) grounding electrode conductor has to be 1/0 AWG minimum [53.5 mm^2].

In IEC World according to IEC 60364-5-52 3*240 mm^2 copper XLPE rated 396 A [underground].

According to IEC 60364-4-41 if line conductor cross-sectional area it is more than 35 mm^2 the protective conductor has to be S/2 [120 mm^2].But in any case the requirement of this formula will be taken into account.

The formula S=sqrt(I"k^2*t)/k

k= SQRT(K20*C*dens/alpha20*ln((1+alpha20*(Tc-20))/(1+alpha20*(Tb-20)))/10^6 [for excel convenience].For copper conductor:

K20cu=56*10^6[1/ohm.m] ;alpha20=0.0039[1/oC];dens=8900[kg/m^3]

Now the tricky point is to choose the right Tc [maximum conductor temperature],Tb=ambient temperature and t=clearance fault time

For a short time of 0.02 to 1 sec. the maximum temperature could be from 150 [pvc insulation],250 [XLPE insulation],1084[bare].

For more than 40 times rated short-circuit current the clearance time it is one cycle [according to most of circuit breaker trip characteristics].So if Isc=25 kA [25/0.4= 62.5 multip.] the time could be 1/50 [IEC World] then for 25 kA 0.02 sec. 150oC maximum 40oC ambient the minimum copper cross-section area will be 27.4 mm^2.

__________________
Julius
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#12
In reply to #11

Re: Earthing Cable Size Calculation

06/15/2015 9:30 AM

thank you, do u know any source to freee download IEC 60364-5-54?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13
In reply to #12

Re: Earthing Cable Size Calculation

06/15/2015 1:16 PM

Sorry, I don't know. However you may purchase it ,I think, only for 8$:

http://www.pdf-standard.com/--iec-c-pdf-standard-41/iec-603645542002-pdf-format-electronic-copy-p-pdf-standard-62568.html.

I did not try it.

__________________
Julius
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#14
In reply to #13

Re: Earthing Cable Size Calculation

06/16/2015 9:53 AM

thanks a lot

Register to Reply
Register to Reply 15 comments