I have a 10MVA and 36MVA data sheet. It has the percentage impedance volts from which i have calculated impedance. But it doesn't mention the copper loss or X/R ratioand hence i don't know how to calculate the values of X and R. Its an important part of my assignment. Any idea how this can be done?
Re: Calculating reactance and resistance of transformer without copper loss data
06/24/2015 3:16 AM
start here: https://en.wikipedia.org/wiki/Copper_loss
Then try this.
The rest is part of YOUR assignment and should be done by you.
Re: Calculating Reactance and Resistance of Transformer Without Copper Loss Data
06/24/2015 11:13 AM
AAsk the manufacturer.
Good Answers: 42
06/24/2015 1:16 PM
In my opinion-I don't know for what purpose you need this-you can take the average shown in ANSI C37.010. See for instance :
http://www.arcadvisor.com/pdf/GET3550Fapp41-43.pdf
Since for this size the ratio X/R >15 the difference between Z and X is negligible-in my opinion.
Julius
Good Answers: 444
06/24/2015 2:20 PM
It's a homework assignment, a real nameplate includes the per unit or per cent impedance and the base quantities that it is based on.