Starting Current Calculation for ATS Starter

07/02/2015 6:06 AM

Dear all,

I want to know that when i will start motor with ATS starter then how much times of FL current it will take during starting. Is it around 3 Times higher then its FL Current?

Regards,

Mehul

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#1

Re: Starting Current calculation for ATS Starter

07/02/2015 9:31 AM

The ATS will normally have tappings at 50%, 65% and 80% voltage levels, but there may be more on some units. Depending on which tapping is selected, starting current will be reduced by 75%, 58% and 36% respectively of that for DOL starting.

As a percentage of FL current, this would be around 150%, 253% and 384% respectively.

The formula for this is:- Ist = (Tr/100)²(Si)

Where Ist =Starting current, Tr = Tapping ratio %, Si = DOL starting current.

Eg, assuming a motor with a full load current of 50 amps and a DOL starting current of 6x or 300 amps and using a 65% tap,

The formula would be:- Ist = (65/100)²(300), = (0.65)² x 300, = 126.75 amps, which is (126.75/50) = 253% of FLC

Starting torque will be reduced by the square of the applied voltage - ie. 25%, 42% and 64% respectively, so the appropriate tapping will need to be selected based on the motor's ability to overcome the load's inertia and to reach around 80% full speed on that tapping. This selection will determine the ultimate starting current for your motor.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Starting Current Calculation for ATS Starter

07/02/2015 3:40 PM

ATS = Automatic Transfer Switch.

Did you mean an RVAT (Reduced Voltage AutoTransformer) starter? If so, then spades' answer is correct, at least in THEORY. In reality, those would be the MAXIMUM starting current. If the load on the motor does not need all of that to accelerate, it would be lower and conversely if the load REQUIRES more than that, it will fail to accelerate and when the starter transitions, the current can still surge to 500-600%, maybe more if the transition is open. In other words it is load dependent.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3
In reply to #2

Re: Starting Current Calculation for ATS Starter

07/02/2015 6:26 PM

You're right about the correct Acronym, but considering that the OP was talking about a motor starter and not a genset, I figured it was safe to assume that he was referring to an auto transformer starter which, although correctly referred to as RVAT starters, are commonly just called ATSs, when talking about starters as the reduced voltage part is a given.

You are also correct about the load dependency, but again the OP was referring to full load current, so I thought it reasonable to assume that full load would be applied.

Maybe I assume too much.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: Starting Current Calculation for ATS Starter

07/02/2015 7:41 PM

And sometimes I too pedantic.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply