Control Building Grounding.

07/02/2015 5:48 AM

Hi,

How is control building (with control panels) connected to earth mat in the case where the control building is located near to the substation. In the case of substation, we can earth equipments by using earth grid of resistance less than 1 ohm, and keeping touch and step potential within limits.

Regs,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Control Building Grounding.

07/02/2015 11:37 AM

You ask the strangest of questions.

This building would be grounded as per any other building, according to the codes and standards in place where the building will be located.

The fact it houses control panels or the fact that it is located close to a substation has nothing whatsoever to do with how the incoming power supply to this building would or should be grounded.

What you may have to pay attention to is how you go about grounding the shields of incoming control cables coming into this building from remote locations.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Off Topic
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2
In reply to #1

Re: Control Building Grounding.

07/02/2015 12:18 PM

Off Topic? Really? How do you figure that?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #2

Re: Control Building Grounding.

07/02/2015 3:45 PM

I agree, I voted that this is not off topic. I guess when you tell someone what they don't want to hear they show how they value your opinion.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Control Building Grounding.

07/02/2015 3:57 PM

Perhaps...

The value of this forum is that often a OP is told what he needs to hear and not what he expects or wants to hear.

I for one will continue to tell them what they need to hear, otherwise what is the point?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #2

Re: Control Building Grounding.

07/03/2015 4:47 AM

It wasn't me but maybe it was because you mentioned control cabling shielding...control of what is the question.

OP may be struggling to describe the switchgear cabin associated with the substation is all.

Now I'm guessing wildly.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Control Building Grounding.

07/02/2015 12:36 PM

There is a good page in Wikipedia on grounding/earthing systems. Well worth a read for the general principles.

The answer may also be found by asking the qualified Electrician who makes the connection to the building.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Control Building Grounding.

07/06/2015 10:36 AM

According to BS 7430 19.2 General earthing arrangement of substations-there are six cases considered depending upon transformer position in the substation-or near-and if the low voltage will be supplied for substation auxiliaries only or for other outside consumers.

Only in one case-when the transformer is not a part of high voltage-medium voltage substation then it is required a maximum 1 ohm ground resistance and 430 V earth potential in a high voltage ground fault case in order to be permissible use a common grounding grid for high and low voltage system. If these conditions are not fulfilled then the low voltage neutral and protection conductor shall be insulated and connected to an electrode located far from the high voltage grounding electrode

- 3 m at least.

If the control building is a part of substation and the distribution transformer is located on major part of the substation and if the possible potential rise exceeds 430 V the major substation should not contain a source of supply to an external low voltage network.

According to IEEE [USA] this grounding is treated differently.

IEEE 80 ch. 17.8 Separate grounding:

"The practice of having separate grounds within substation area is rarely used. "There are many disadvantages.

ch.17.9 Transferred potentials:

This transferred potential may be transmitted by communication lines, rails, conduits, low-voltage neutral etc.

17.9.3 Low-voltage neutral wires

This neutral wire shall be treated as "live" and insulated for possible GPR or transferred potential.

__________________
Julius
Register to Reply