Parallel Cummins Generator

07/05/2015 7:11 AM

I have 4 Gen. Cummins with PCC-3100 , need to connect them in paralleling .

when i start first one by signal from ATS , how can start 2nd one,3rd and 4th reference to load

and about synchronizing between gen's. depend only on communication between

generators ?

Hope help me

Register to Reply
Pathfinder Tags: Generator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Parallel Cummins Generator

07/05/2015 7:53 AM

Tell me what the generator manufacturer said during your last few phone calls.

__________________
Good moaning!
Register to Reply
Member

Join Date: Jul 2015
Posts: 9
#3
In reply to #1

Re: Parallel Cummins Generator

07/05/2015 10:31 AM

I contact with manufacture by email and he ask me to contact with distributer im my country but .

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4
In reply to #3

Re: Parallel Cummins Generator

07/05/2015 12:01 PM

Again, how did your last couple of TELEPHONE CALLS go, Mildred?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2

Re: Parallel Cummins Generator

07/05/2015 9:16 AM

I expect that you would require an automatic load demand control module, likely called something else by Cummins, but most manufacturers offer them for load demand based auto starting of parallel gensets.

They generally have all of the communication and sync processes on board and should be a simple add on to your existing control modules.

Register to Reply
Member

Join Date: Jul 2015
Posts: 9
#5
In reply to #2

Re: Parallel Cummins Generator

07/05/2015 12:49 PM

PCC-3100 is generator controller and its include parallel feature but this point not clear i mean exactly how multi genrators will run if master one run from ATS ,what about another generators how run refernce to load .

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#8
In reply to #5

Re: Parallel Cummins Generator

07/05/2015 5:22 PM

Whilst it can handle paralleled gensets, I don't think that the PCC-3100 control has the capability to run load demand controls for them.

As I stated earlier, you will likely require an add on module for that bit.

Cummins calls their module a "Masterless Load Demand (MLD) upgrade kit"

It wasn't hard to find...Go to this Cummins site for info...Page 15 tells you about it.

Then do as others have suggested and contact the supplier.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Parallel Cummins Generator

07/05/2015 12:54 PM

The forum cannot do your work for you.

This should have all been done at the time of purchase of the generators.

Call this number: 1-812-377-3000 and tell them you NEED HELP.

Quit wasting time and get on the phone or go here:

Customer Assistance | Cummins

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Parallel Cummins Generator

07/05/2015 1:24 PM

The word for today is "synchroscope"; but if your budget is too cheap, you can do it with three lights and as many switches as generators.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #7

Re: Parallel Cummins Generator

07/06/2015 12:38 AM

1 lamp is all you need as long as it can withstand full phase to phase voltage otherwise 2 lower voltage lamps in series does it. Could use a Voltmeter too.

Provided the DGs are rotating the same way then if one phase is synced then so are the others.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: Parallel Cummins Generator

07/06/2015 12:59 AM

The three lamps can also cover the case in which one or more gensets are accidentally connected in wrong rotation. You or I might not do that, but the OP is questionable.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Jul 2015
Posts: 9
#11

Re: Parallel Cummins Generator

07/06/2015 2:15 AM

the lamps is not my problem , where the controller can synchronis its output reference to bus(load) voltage and frequency .

the matter how start the genset regard to load , im looking to run follow one based one load demands , and ask my controller has the feature or not if not i will use current transducer connect to plc.

regards

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#12
In reply to #11

Re: Parallel Cummins Generator

07/06/2015 6:50 AM

click the link provided by Spades in reply #8

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#13
In reply to #11

Re: Parallel Cummins Generator

07/06/2015 1:30 PM

Do you know how to use a telephone?

__________________
Good moaning!
Register to Reply
Member

Join Date: Jul 2015
Posts: 9
#14
In reply to #13

Re: Parallel Cummins Generator

07/07/2015 5:53 AM

waiting you to inform me how

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#15

Re: Parallel Cummins Generator

07/07/2015 7:45 AM

According to the brochure ( have you read post #8 yet?) on page 3 the PCC3300 will do that which you ask in combination with the PowerCommand 3.3 MLD on page 15.

A nice HMI would make it slick.

To upgrade the 3100 ( to work as you desire) you need to read pages 6 through to 14. It's all spelt out for you.

A glance at your 3100's manual would be a prudent move. Go crazy and read the generator and sync panel manuals while your at it.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Member

Join Date: Jul 2015
Posts: 9
#16
In reply to #15

Re: Parallel Cummins Generator

07/10/2015 10:29 AM

I will use current transducer to get analogue signals and regargard signal i will start and stop genset useing PLC .

Analogue sinals will indicate the load amount

Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (3); lyn (1); MBROTHER (5); spades (2); Tornado (2); Wal (3)

Previous in Forum: Useful Online Calculator Website   Next in Forum: Shell Type Transformer Not Performing as Expected on Low Power Input

Advertisement