Ice Cub

07/12/2015 12:58 PM

I read an article in the business section of the local newspaper. The article is about the Ice Bear system. It is a cooling system that works in conjunction with a typical a/c system to reduce on peak cooling cost to the electrical rates of off peak costs.

Essentially it is a ice maker / ice storage unit with automatic control module that shuts down the primary a/c cooling unit and it looks to use ice to cool the high pressure liquid side.

The technical information says that it has a capacity of 6 hrs before ice is melted or reaches 48*F. The reservoir tank is to be filled with tap water annually ( it seems tap water would need to have a low concentration of precipitates to prevent scaling & could distilled water be substituted ?)

6 hours doesn't seem long enough as the summer temps can be at 90*f + at 09:30 to 19:00 .

I wonder about cost per unit, installation cost, 20 year unit factor, return of cost expenditure, maintenance and service cost to make viability for residential application.

Thought there might be engineers here with opinions here on this.

www.ice-energy.com/technology/ice-bear-energy-storage-system/

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Ice Cub

07/12/2015 1:10 PM

It depends. In a large office building or a NEW house, maybe. Although chilled water may work as well in large buildings.

I liken it to pumped storage generation of electricity. Use electricity when the demand is low to make ice/pump water back into a reservoir. Then when demand/cost is high use the ice/water over again in place of more expensive electricity.

It's strictly a cost/benefits study.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Ice Cub

07/12/2015 1:49 PM

I've actually been to their offices and talked to them....its an electrical load shifting strategy

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#3

Re: Ice Cub

07/12/2015 2:46 PM

I have suggested the same principle for air conditioning electric vehicles - generate a cold sink (a mass of material of high specific heat) during the night charging period and draw on it during the day, thus saving the battery for motive power. The same principle may be used for heating the vehicle in the winter.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #3

Re: Ice Cub

07/12/2015 2:51 PM

have you ever calculated the energy required to drag that around? the returns diminish with every pound

Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#5

Re: Ice Cub

07/12/2015 4:26 PM

This idea was done in the 20s-30s, mainly for large intermittent human occupations like theaters. It allowed a much smaller refrigeration unit, that froze water in large tanks located in the basement. Some of these are still operational.

Humans emit lots of heat, both sensible, and latent.

__________________
ignator -
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6
In reply to #5

Re: Ice Cub

07/12/2015 4:38 PM

A ton of refrigeration (commonly abbreviated as TR) is a unit of power used in some countries (especially in North America) to describe the heat-extraction capacity of refrigeration and air conditioning equipment. It is defined as the heat of fusionabsorbed by melting 1 short ton (2,000 lb; 0.893 long tons; 0.907 t) of pure ice at 0 °C (32 °F) in 24 hours.[1][2] It is equivalent to the consumption of one ton of ice per day and originated during the transition from stored natural ice to mechanical refrigeration.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Ice Cub

07/12/2015 6:58 PM

The JRT (Japanese Refrigeration Ton) is similar, but based on a metric tonne (2204 lb) of ice/water.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Ice Cub

07/12/2015 7:39 PM

Like most energy usage time shifting systems it depends heavily upon the electric rate differential between daytime and night-time so that you can recover the capital costs.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9

Re: Ice Cub

07/12/2015 10:15 PM

I don't believe this would save any energy, but merely shift the electrical load from day to night...also don't believe it would last 6 hrs....in any case the ability to cool would diminish as the heat load increased throughout the day which peaks at about 4:00 pm...add to that the costs, both initially and maintenance and repair, and you have a higher cost of ownership, a more complex system adding to longer troubleshooting times and costlier repairs....Now this probably works for the utilities as it's intended, but if the maintenance and repair is the responsibility of the equipment user or you have to call the utility( god forbid) to do the repair, well I see a problem...and if the cooling diminishes in the afternoon, you're going to have some unhappy people, in fact you're going to have to deal with very nasty feedback, which throws the service personnel under the bus, which will make servicing these accounts unpopular and difficult....I'd have to see it in operation over a period of time to be a believer...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #9

Re: Ice Cub

07/12/2015 10:23 PM

it augments an existing unit, using the existing air handling, its simply a block of ice if the stat calls you use the same mechanical cooling. its quite simplistic, the biggest problem they had when I met them was dealing with the weight of the ice on a roof, they needed to be close to a column or gluelam or construction costs quickly shot up.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #10

Re: Ice Cub

07/12/2015 11:07 PM

On the roof!?! Exposed to losses from the ambient temperature, wind, and solar insolation...I know it's insulated, but that's the worst place to put a block of ice, don't think there's going to be much savings from this unless the rate differential is at least 5 to 1, closer to 10 to 1 for any reasonable payback period.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#17
In reply to #12

Re: Ice Cub

07/13/2015 9:30 AM
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #9

Re: Ice Cub

07/12/2015 10:33 PM

It can work, unless electricity is the same price all the time.

It's the payoff that's the question.

Here in Arizona we have different rates for different of the day.

Case Studies

How it Works

Not an endorsement, just sayin'.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #11

Re: Ice Cub

07/13/2015 1:40 AM

Those are case studies in name only, they give no specific information....They say they saved x amount of electricity but also say the A/C units were upgraded to high efficiency, but doesn't differentiate what saved how much...450 gallons of water = 3600 lbs...sort of like parking a car on the roof....There's no maintenance costs mentioned...no feedback from users...that much water freezing and thawing on a rigorous schedule like this is going to cause a lot of wear and tear on the containment area....I know enough about refrigeration to know that cooling the refrigerant in a liquid state and using that as a cooling medium is not the same as a true refrigerant cycle of evaporation and condensation, therefore I would question the performance of the unit in this mode....twice as much equipment means twice the problems...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#18
In reply to #13

Re: Ice Cub

07/13/2015 2:47 PM

"I know enough about refrigeration to know that cooling the refrigerant in a liquid state and using that as a cooling medium is not the same as a true refrigerant cycle of evaporation and condensation"

I believe you misunderestimate the process in use here.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#19
In reply to #18

Re: Ice Cub

07/13/2015 3:54 PM

The magic fakes plase during phase changling....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#21
In reply to #19

Re: Ice Cub

07/14/2015 2:34 PM

You missed the part about the "true refrigerant cycle of evaporation and condensation.

That hasn't changed.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#14

Re: Ice Cub

07/13/2015 4:04 AM

They call them ice builders in factories, normally around 1mx1mx1m gives a tonne of cooling if all you need is cold water on demand.

If you have off peak electricity tariffs and the space and capital and maintenance budget....and you need loads of cooling that will offset the capex through tariff savings then it's good.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#15

Re: Ice Cub

07/13/2015 9:07 AM

The best energy saving I found is when I installed a large desuperheater on my heat pump to heat mu pool instead of using a second heat pump like most people around here. I also have a desuperheater for the household hot water circuit.

Now, when I cool the house, the heat is dumped in the pool until 31C. Afterward, the normal air coils takes over and sends the surplus heat outside.

I don't understand why all house with AC systems or hotels or other buildings don't produce most if not all their hot water from the AC system in the summer.

It was so easy to do once I found an AC tech who would stop worrying about the warranties. It has been running for ten years. That was the best $2000 spent I could come up with. I save about that much in electricity each ~18-20 months.

I have other energy saving systems such as grey water and air exchange heat recovery but don't get the same return on my investment (if any).

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#16
In reply to #15

Re: Ice Cub

07/13/2015 9:13 AM

if you don't already...pipe the condensate line from the AC coil into your gray water rather than down the drain its an easy 5-20 gallons a day when humid

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#20
In reply to #16

Re: Ice Cub

07/14/2015 1:15 PM

Good idea for those who live in an area poor in fresh water.

I live in Montreal, Quebec. It is an island surrounded by fresh water. Some people talk about wasting water but is is an imported green concept that doesn't apply to us.

We only have a limit on the treatment plants capacity. Anyway, half of the treated water leaks out of the distribution system. They could start there if they want to "save water".

Our water usage is as follow:

The water treatment plants take the raw water from the river. Clean it up and we use it.

When we flush the toilet, it goes to another plant that clean it up again before returning it to the river.

When we water the grass or garden, most of it percolates in the soil and most likely ends up back into one of the rivers around the island. The only water loss is by evaporation and it most likely falls back as rain nearby.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Off Topic (Score 5)
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

energyconversion (1); Fredski (6); ignator (1); lyn (4); marcot (2); RAMConsult (2); SolarEagle (3); Tornado (1); Wal (1)