Gents, I have one 220 volts 0.75 kw single phase motor and that motor's capacitor was damaged. unfortunately I couldn't get any details from that capacitor. So anybody can tell how I can calculate that capacitor? Please tell the formula. The motor split phase motor.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#1

Re: capacitor calculation for single phase motor

07/13/2015 6:33 AM

This document has some general information:

http://www.kemet.com/Lists/ProductCatalog/Attachments/158/F9000_GenInfo_MotorCaps.pdf

If you have a nameplate on the motor, the safest thing would be to do a search on that or contact the manufacturer.

Reply Good Answer (Score 2)
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#4
In reply to #1

Re: capacitor calculation for single phase motor

07/13/2015 7:57 PM

Be a bit careful about the charts at the end of that website, they don't relate to start caps.

Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#2

Re: capacitor calculation for single phase motor

07/13/2015 6:33 AM

Such a formula involves much more than voltage and power. So better Google the exact motor model for hints or push your lack and use a ~15uF 500V AC RUN (not start) cap. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Reply
5
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3

Re: capacitor calculation for single phase motor

07/13/2015 7:26 AM

Is there any information on the motor name plate?

Is the capacitor a start, run, or permanent split type? You need to know this before going any further.

How to decide:-

1. If there is a centrifugal switch, then it won't be a permanent split cap.

2. If there is a centrifugal switch and there is only one cap then it is most likely a start cap, and whilst you can use a run cap in lieu of a start cap, the size required is much larger and may not be a realistic option.

3. If there are two caps, then one will be a start cap and one will be a run cap, the larger one will be the start cap. You can verify this by metering the wiring...The start cap will be disconnected from the circuit when you open the centrifugal switch.

Assuming it's a start cap, then a good guess for that size motor would be around 100 microfarad.

The formula is:- C = (I*106)/(2π*f*V)

Where C =capacitor size in microfarads, I = full load current in amps, π = pi = 3.14, f= supply frequency, V = supply voltage.

This should give you a figure around 100 - 120µf. Note that start caps do not have a specific size as do run caps, they have a range. Get one within that range and you will be OK.

The cap should have a voltage rating of at least 360 volts.

Reply Good Answer (Score 5)
Anonymous Poster #1
#5
In reply to #3

Re: capacitor calculation for single phase motor

07/14/2015 4:54 AM

Thanks for your reply. this motor is not capacitor start motor and this one is split phase motor so the capacitor is permanently in line. The motor capacity is 0.75 kw and 220 volts and this one is ex proof so i couldn't get the capacitor value from the capacitor body (fully covered with plastic).

Reply Off Topic (Score 5)
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6
In reply to #5

Re: capacitor calculation for single phase motor

07/14/2015 5:51 AM

You probably need to get your terminology in order so that we can understand your problem...a split phase motor can appear in any number of guises, capacitor start being just one of them.

Being explosion proof doesn't exclude it from being capacitor start, it just may be that the start gear (timer) is remote from the motor.

If you are trying to tell us that it is a permanent split capacitor motor, then the cap size would be somewhere around 20 to 30 microfarad and minimum 360 volt. Make sure it's not an electrolytic type.

Reply Off Topic (Score 5)
Anonymous Poster #2
#7

Re: Capacitor Calculation For Single Phase Motor

04/10/2020 10:16 AM

Capacitor Calculation For Single Phase Motor

Reply Off Topic (Score 5)
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Rixter (1); SimpleMind (1); spades (3)

Previous in Forum: The Reflected Wave Phenomenon   Next in Forum: Screen Issue

Advertisement