HYDEL/Thermal Generator

08/05/2015 10:32 AM

HOW ROTOR INERTIA GD2 FOR HYDEL & STEAM AC GENERATOR (SAY 11KV,5MW) CALCULATED?

ROTATING MASS FOR HYDEL & STEAM GENERATOR,HOW IT DIFFERS FOR THE SAME RATING OF AC GENERATOR (SAY 11KV,5MW)?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: HYDEL/Thermal Generator

08/05/2015 1:05 PM

It's called the "H-constant" and there is plenty of information available on the web. It is a function of the rating of the machine, it's rotating masses and their placement, and speed.

Hydroelectric (HYDEL) generators are vastly different than steam turbine driven generators; slow versus fast, short and squat vs. long and slender, salient pole vs. round rotor, vertical vs horizontal, etc., etc.

The GD² is usually provided by the manufacturer, it is a physical constant that is calculated by mechanical engineers familiar with the construction of the rotor. You will find charts comparing the different values vs type of rotor on the web.

I hope that you didn't shout during the interview, questions like that enable a skilled interviewer to immediately disqualify an unknowledgeable interviewee.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Participant

Join Date: Aug 2015
Posts: 2
#4
In reply to #1

Re: HYDEL/Thermal Generator

08/22/2015 5:28 AM

Sir,

1) which components in Hydel generator makes costlier than thermal generator?

2) How the Speed rise & pressure rise is controlled in Hydel/Thermal Generators when the full Load on the Generator is thrown off? ( during Tripping due to faults)

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: HYDEL/Thermal Generator

08/23/2015 1:37 AM

1) is open ended, you are making the assumption that one is more costly than the other without stating what you are comparing; i.e., are you referring to the electrical generator itself, including the turbine, the BOP (Balance Of Plant), the fuel source, the power transmission equipment, and/or any combination?

2.) Are you questioning if the inertia of the rotating mass somehow causes it to overspeed during a full load rejection? If so then you are under a common misconception since it does not. Think about it, inertia is the physical property that keeps a body in motion, in motion, until it is acted upon by an outside force.

Where does that force come from, certainly not from the rotating mass since it is inert and has no internal source of power. It comes from the inertia of the residual fluid driving the turbine; i.e., what ever water is still in motion in the penstock after the sluice gates slam closed, or whatever steam is still entering the turbine from the steam chest after the emergency stop valves slam shut. All of this presumes that everything is operating properly prior to, during, and after the emergency trip is initiated.

Most people who have never had the chance to analyze, model, witness, or test the multiple systems that go into the overspeed trip mechanisms will immediately respond with "No, can't be, what happens to all that energy stored in the rotor, it HAS to go somewhere and it HAS to go into making it turn faster post-trip..." I know first hand, because that was my exact reaction when I started writing programs (in BASIC!!) for modeling the second and third order dynamic effects.

Here's a mind experiment that may help. Consider a machine that's at synchronous speed just prior to closing the breaker, just enough steam/water is being admitted to overcome friction and windage. What would happen if the valves were closed? Think of the forces acting on the rotating mass, a very small amount of low pressure steam/water just overcoming the rotational losses, take away that pressure and the only force left is friction, and it can only SLOW things down, it's a decelerating force! There is no accelerating force to make it go faster. If you're still troubled by this then take the time to calculate the stored energy in an unloaded vs. fully loaded machine.

So why do machines overspeed? Because somebody, something, or both, screwed up and didn't stop the flow of steam/water. The operator admitted too much steam when the safeties were blocked, the governor wasn't set properly, the emergency stop valves jammed, the clearances weren't checked/set properly, a jumper wasn't removed (happened to me), a relay got stuck, a subsystem was tagged out, the operator had a "heavy" hand, a technician dropped a screwdriver, the backup systems were on the same DC supply as the main systems which happened to fail, etc., etc.

I hope this helped, class dismissed.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#2

Re: HYDEL/Thermal Generator

08/05/2015 1:13 PM

I'm sorry, I can't hear you when you are yelling.

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: HYDEL/Thermal Generator

08/05/2015 1:51 PM
  1. Start by turning off Caps Lock.
  2. A Google search on "inertia GD2" produced 13,000 results in 0.42 seconds, including a methodology for doing it. So, that's probably the next step.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: