Anonymous Poster #1

A New DP Flow Meter

08/07/2015 1:40 PM

Hello

I want to install a new Dp flow meter (Orfice plate) for measring a supersteam ,the old one (Dp flowmeter) didnot work well , So I want to change it :

1- The teamparture is : 400 to 450 degree c

2- The range in the plc : 0 to 1400 kg/h , Uesally is reading between :122 to 300 kh/h

How can I choose a new Dp accorrding what ?

How can I make a calbration according to that specified on the plc (0 TO 1400)KG/H

Pls I need your advices about this topic ASAP

Best wishes

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: A new dp flow meter

08/07/2015 1:56 PM

Contact the DP flow meter manufacturer of you choice and discuss your application requirements in detail with them.

Be sure that you reveal all issues you are currently having as well as any issues you have had in the past with the existing meter.

Be sure to provide details on the installation such as pipe diameter, type of fluid being measured, temperature ranges, pressure ranges, all obstructions and restrictions, quantity of valves, location of valves, flow ranges, ambient temperature and humidity conditions, altitude, etc.

You will most likely be asked to complete a standard meter installation sheet and/or provide an up to date P&ID drawing.

If you do not understand all of this, I suggest you hire a competent technical person to go to your site and perform an analysis on the application.

Once you get their recommendation then follow their advice thoroughly.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Score 1 for Good Answer
3
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: A New DP Flow Meter

08/07/2015 8:10 PM

Apparently the DP flow transmitter is working, but the results aren't satisfactory. No surprise, you have at least one issue, probably two.

Issue 1: If your readings typically max out at 300kg/hr, why do you think you can use a 0-1400 Kg/hr span?

DP technology has a very low turndown, typically no more than 4:1, which means that the useable accuracy of a 0-1400 span is between 360 kg/hr and 1400 kg/hr (360 = 1400/4). Accuracy drops off and noise increases dramatically at flow rates lower than the lower end of the turndown, that is, lower than 360kg/hr

What is your observed maximum flow rate?

If your observed flow rate is near or below 50% of the 1400 flow rate, you need to get a new orifice plate sized properly to your observed max flow rate. Orifice plates are relatively cheap, DP transmitters are relatively expensive. Then your re-range your existing DP flow meter to the new orifice plate.

Issue 2: You mention "measuring supersteam". If you mean 'measuring super heated steam', then your DP transmitter is incapable of providing accurate readings because plain DP cannot take into account the added heat in superheated steam. DP is fine for measuring saturated steam because temperature and pressure are dependent variables for saturated steam. But with superheated steam temperature and pressure are independent variables and need to measured independently and applied to the calculation for a mass flow rate value.

That is done with either a 'multivariable transmitter' or a flow computer because either requires separate DP, absolute static pressure and temperature measurements, all of which are used in a calculation to derive a compensated mass flow value.

Multiple xmtrs, flow computer on the left
Multivariable on the right

DP technology infers a volumetric flow from a differential pressure and line size, but it does not infer mass flow. DP is traditionally used for saturated steam flow. The units of mass flow, kg/hr are assumed by the host system's scaling. A multivariable measurement is an inferred mass flow measurement, not an assumed mass flow measurement with just a mass flow label.

As an aside, 'ASAP' is probably what produced your current results. Thorough and methodical engineering will give better results than haste.

Reply Good Answer (Score 3)
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#3

Re: A New DP Flow Meter

08/10/2015 3:15 PM

You may want to try http://www.flexim.com/us?gclid=CJ7dv5Cbn8cCFYiPHwodycIH9A to try an alternate DP flow meter technology.

Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#4

Re: A New DP Flow Meter

08/11/2015 11:33 AM

Flexim clamp-on ultrasonic for steam flow? really? I am unaware than any clamp-on ultrasonic does steam flow rate.

Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5

Re: A New DP Flow Meter

08/11/2015 5:40 PM

Do you really want to do that, or do you want to go vortex shedding instead?

__________________
Good moaning!
Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); Iris (2); SHOCKHISCAN (1); welderman (1)

Previous in Forum: Where is the Leak?   Next in Forum: Multispot Temp Element

Advertisement