Earthing Value

07/19/2007 2:56 AM

Dear friends

Please can any one tell me the maximum earting value for a DCS or PLC system and for the field instruments (shield cable)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Earthing Value

07/19/2007 4:18 AM

10 ohms?

Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#2
In reply to #1

Re: Earthing Value

07/19/2007 7:06 AM

<1 ohm

__________________
BNDas
Reply
Commentator

Join Date: Aug 2011
Posts: 76
#6
In reply to #2

Re: Earthing Value

08/24/2011 1:50 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply Off Topic (Score 5)
Anonymous Poster
#3

Re: Earthing Value

07/20/2007 1:49 AM

The smaller the better, but a value ≤ 4 Ω is acceptable. Make sure that the earthing of your PLC and the instrument screen/shield have an earthing system separated from the structural (equipotential) and electrical earth. So do not connect to the earthing of the panel because this has to be structural earth. All this systems should only at the real earthing point (rod or grid) come together. Star principle.

Reply
Anonymous Poster
#5
In reply to #3

Re: Earthing Value

11/18/2008 12:30 AM

Can you please tell us that the value ≤ 4 Ω is recommended by BS,IEE.If yes can you give us the relevant pages Please.

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: Earthing Value

07/21/2007 3:38 PM

I suspect the earthing method and location is equally important. Frequently in the product documentation I have read, the earthing (grounding) conductor has a minimum size that can be greater than the circuit or signal conductors---necessary for proper control of the low-level signals which are protected by it. The source and type of interference or noise needs to be considered, particularly if it is a nearby power conductor.

I had a very vexing problem in a PLC panel with 4-20mA analog signal cables and a small variable frequency drive (VFD) for the equipment's conveyor motor. The electrical noise and control errors were reduced when the earthing conductor for the motor was moved to the VFD's output earthing terminal instead of the control panel's nearby earthing terminal, but were eliminated only when I replaced the power conductors with a shielded power cable and similarly earthed the shield in the VFD. I had already taken the precautions of running the cables in separated wireways and separate conduits, etc.

JMM

Reply