Static charge measurement

07/19/2007 8:52 AM

Agree with comments from TRRao. We can not measure the static charge directly but can use indirect measurements using static charge meters which measures the surface potential in kV. We recently used a Surface DC voltmeter and obtained the potential in kV. It was supplied by Alpha labs Inc., USA. You may wish to contact them.

We had three static related flash fires while loading trucks with Xylene, all three happened in summer and in one gantry only. It made us to check the gantry earthing system thouroughly and found that the bonding reel did not make contact with the bonding drum occassionally. The tanker purging with Nitrogen was not adequate leaving a flammbale atm inside the tanker. The product pumping rate was at 2 m/sec linear velocity only. The truck earthing lug was found corroded hence did not make a contact with grounding system of the gantry ocassionally, depending on how one fixes the grounding clip. So of the four steps needed for a static charge to ignite a vapor, we had three steps established through measurement/tests. The only questionw as where from the spark jumped. The loading lance/pipe was of SS and was touching the tanker bottom and the lance was bonded with the gantry structure. The structure was earthed at four earth pits. The Er values were perfect < 10 Ohms.

Still there was an igntion inside the tanker which now we think was caused by a spark gap between the liquid and the lance surface or between the manhole and the lance.

Q. Is it possible for a spark to jump between the lance and liquid surface though the lance is surround / submerged in the liquid?

Q. If the spark is assumed to occur on the top of the tanker between the tanker manhole and the lance, where was the flammable vapour at the manhole cover. Our readings show the LEL was less than 2% on the top during a simulated drill. The charing pattern on the lance indicated that the fire started at the botom and spread to the top.

Can some one advise me on where could have been the spark gap and between what?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Static charge measurement

07/19/2007 9:02 AM

Q. Is it possible for a spark to jump between the lance and liquid surface though the lance is surround / submerged in the liquid?

A: Turn it to the stable-2 position: imagine a lightning arrestor in a thunderstorm and there you have it.

__________________
Good moaning!
Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#2

Re: Static charge measurement

07/20/2007 12:10 AM

Formation of spark alone may not cause explosion. For fir to take, place, the good amount of fuel and air mixture must exist, there after, temperature also starts playing greater role and it becomes an explosion, which sends shock-waves, dispersing the liquid in open air and heating adiabatically and making it a greater fire ball. Simple ignition may burn for many days and may not be intense explosion at all.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: Static charge measurement

07/24/2007 8:33 AM

I hope in unloading zone some sort of air draft arrangement should be maintained, to make is zone 2. This is to take away potential gas accumulation during unloading.

__________________