Interconnecting Transformer/DG Neutral Earthing with Main Earth Grid

09/03/2015 6:57 AM

Hi,

I have following questions regarding earthing system.

1. Should we interconnect transformer/DG neutral earthing with main earth grid in project premises or not?

The inter connection is to be done below ground level.

Above ground level separate neutral earthing strips are provided to neutrals & electronic items.

Please note/consider following

1. 3150KVA 11KV /0.433KV - DYn11 TR - solidly earthed neutral

2. 1500KVA DG with solidly earthed neutral

3. TN-S earthing system is implimented

4. All the equipment body, machinery, lightning protection, electronics earthing is connected to main earth grid.

5. 11 KV system earthing is separate grid.

6. System Resistance is <1 Ohm

Following are the reference from various standards

IS 3043, page 12, Figure 3 shows neutral earthing connected with body earthing,

IEC 61000 confirms connection of power, electronics, lightning protection earthing together.

IE Rule 61 (Now CEA Safety Regulations) says Neutral conductor of a 3 phase, 4 wire system and the middle conductor of a 2 phase, 3-wire system shall be earthed by not less than two separate and distinct connections with a minimum of two different earth electrodes or such large

number as may be necessary to bring the earth resistance to a satisfactory value both at the generating station and at the sub-station. The earth electrodes so provided, may be inter-connected to reduce earth resistance.

IE Rule 61 IMPORTANT [[[[[ It may also be earthed at one or more points along the distribution system or service line in addition to any connection with earth which may be at the consumer' s premises.]]]]]

Above rule is applicable to LV distribution system as well. So, if From electricity board transfomer earthing is provided and that earthing is connected with earthing pit/bus in consumer premises than it is as good as connecting TR neutral with main earth grid in single project premises.

Cl. 9.10.12.2 of IEEE 1100, "the use of any separate, isolated, insulated, dedicated, clean, quite, signal, computer, electronic or other such improper form of earth grounding electrodes for use as a point of connection of the EGC (Equipment Grounding Conductor) is not recommended".

Cl. 5.5.4.5 of IEEE 142, 'The NEC requires that all equipment served from an electrical source be grounded or bonded to the grounding point of that source.

BUT THE PROBLEM IS - It is general practice to keep neutral earth pits separate from body earth pits and not to connect these neutral earth pits with main earth grid (below ground).

I am not sure why this practice is followed as it may have implications.

For example In TN-S system when there is earth fault in any equipment current returns via body > earthing conductor > earthing grid > neutral. The heavy current passing during this trips the circuit breaker. Also, the potential of the equipment body with reference to ground (touch potential) stays within limit (say less than 50 V).

Now if there is no connection between main earth grid and transformer neutral than return current has to pass through earth. If the earth resistivity is higher, resistance of return path will increase, which may give higher touch potential. Also, connecting equipment body with neutral is the fundamental requirement of TNS system which also won't be fulfilled.

Please provide your suggestions/inputs/justifications/logic (with examples/calculations if possible).

Thank you in advance.

Jatin

Register to Reply
Pathfinder Tags: earthing Earthing grid
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Interconnecting transformer/DG neutral earthing with main earth grid

09/03/2015 7:13 AM

A possible source of information is "The Soares Book on Grounding and Bonding", plus the requirements of your local jurisdiction.

There are different schemes and rationales about this, each of which may have advantages and disadvantages, but consistency within a region is important, whichever scheme is adopted.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Sep 2015
Posts: 5
#2
In reply to #1

Re: Interconnecting transformer/DG neutral earthing with main earth grid

09/03/2015 7:19 AM

Hi Tornado,

Thank you for prompt response

I got your point that local standards shall be followed. I have given details of various standards just for reference.

I am looking for right justification of the problem "whether we should interconnect Neutral & Body earthing or not?"

Jatin

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3
In reply to #2

Re: Interconnecting transformer/DG neutral earthing with main earth grid

09/03/2015 7:33 AM

he already told you! check your local requirements for specific instructions

Register to Reply
Member

Join Date: Sep 2015
Posts: 5
#4
In reply to #3

Re: Interconnecting transformer/DG neutral earthing with main earth grid

09/03/2015 7:39 AM

Hi Fredski,

I am looking for right justification of the problem "whether we should interconnect Neutral & Body earthing or not?"

Thanks

Jatin

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5
In reply to #4

Re: Interconnecting transformer/DG neutral earthing with main earth grid

09/03/2015 3:02 PM

You don't meet to look any further than the phone number of a local qualified electrician, Mildred. If "we" don't know what to do, then this individual surely will.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6
In reply to #2

Re: Interconnecting transformer/DG neutral earthing with main earth grid

09/03/2015 7:14 PM

I would think it would be mandatory to bond the DG neutral earth/ground to the system earth/ground grid for personnel protection safety reasons.

If you do not do so how you will the system have any ground/earth fault protection?

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Member

Join Date: Sep 2015
Posts: 5
#8
In reply to #6

Re: Interconnecting transformer/DG neutral earthing with main earth grid

09/04/2015 12:29 AM

Dear Shockhiscan,
You are absolutely right. I am of the same opinion. But, here in Gujarat, India contractor's general practice is not to interconnect.
I am using TN-S system in which return path is through body > earth grid > neutral
If we implement TT system than only Neutral would be separate.
Thank you.
Jatin

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: Interconnecting Transformer/DG Neutral Earthing with Main Earth Grid

09/03/2015 10:31 PM

"...BUT THE PROBLEM IS - It is general practice to keep neutral earth pits separate from body earth pits and not to connect these neutral earth pits with main earth grid (below ground)..." Where are you located?

The only thing that matters to you is what the AHJ (Authority Having Jurisdiction) has to say about it. If you want to make him laugh tell him that a bunch of strangers on the internet said it was OK.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: Sep 2015
Posts: 5
#9
In reply to #7

Re: Interconnecting Transformer/DG Neutral Earthing with Main Earth Grid

09/04/2015 12:32 AM

Dear RamConsult,

I am based in Gujarat, India. Here it is general practice not to interconnect neutral & body earthing.

AHJ (Electrical inspector here) says you should implement as per CEA safety regulations..... which is like local safety standard...and it is not clear about this particular issue.

Thanks

Jatin

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #9

Re: Interconnecting Transformer/DG Neutral Earthing with Main Earth Grid

09/04/2015 9:22 AM

Since you have never done this before, you should seek the services of a local electrical engineer who has, and can for a fee, provide a written analysis for you. Take that to the AHJ and get his approval. It would be unethical for anyone with no local knowledge to provide support for an issue that can prove to be quite costly if it does not satisfy the AHJ, or deadly if it is implemented incorrectly.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply