Anonymous Poster #1

Excitation Transformer

09/12/2015 9:02 AM

Dear sirs,

The purpose of excitation transformer is to give required amount of dc current to the hydrogenerator field winding.

But it appears that kVA rating of excitation transformer is different for brushless and static excitation system. How is the sizing done for both the cases?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Excitation Transformer

09/12/2015 12:29 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Member

Join Date: Jan 2019
Posts: 9
#8
In reply to #1

Re: Excitation Transformer

04/16/2019 4:38 AM

Sir, the above url is not working. I request you to notice the change. New url

https://electengmaterials.com/static-excitation-of-an-alternator/

Please remove the old url.

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Excitation Transformer

09/12/2015 1:36 PM

They are different because there are major differences in the power demands between the two systems. In a brushless excitation system the power required for the main field is provided by the prime mover, while in a static excitation system the DC power is produced by stationary (hence the name "static") power components that feed DC through brushes directly to the main field.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Anonymous Poster #1
#3
In reply to #2

Re: Excitation Transformer

09/12/2015 7:50 PM

How is excitation transformer rating determined? (both in case of static excitation and brushless excitation?)

Regs,

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #3

Re: Excitation Transformer

09/12/2015 9:55 PM

Like any other transformer, by determining the total current drawn by the connected circuit. For brushless the bulk of the power goes into the control field(s) of the PMG (Permanent Magnet Generator), whose output gets rectified and applied directly to the main field. For static the output goes directly into the field so the input rating of the transformer is basically equal to the power consumed by the main field, plus losses. In either case the control electronics and AVR (Automatic Voltage Regulator) are electronic and take a very small percentage of the transformer's rating.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Anonymous Poster #1
#5
In reply to #4

Re: Excitation Transformer

09/12/2015 10:17 PM

but why is the kVA rating of excitation transformer larger in case of static excitation than the kVA rating in case of brushless excitation?

eg For a generator of 13000 kVA, 428 rpm, what will be the excitation transformer kVA rating?

Regs,

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #5

Re: Excitation Transformer

09/12/2015 11:44 PM

We're sorry, but your free tutoring trial has run out, you will now have to invest your own time, effort, and initiative to research the answers that you desire. The University of Google is your friend, learn how to use it.

Hint: It will be vastly different between scenarios. When all else fails, contact the vendor.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#7

Re: Excitation Transformer

09/14/2015 3:13 AM

It seem that you are getting confused between excitation power requirements and excitation transformer rating. There is no excitation transformer in Brush-less excitation system. It is there only in static excitation system where a part of generator output power is stepped down and after rectification fed in excitation circuit (with necessary control circuit). In brush-less excitation system as stated in other reply, excitation power is developed by coupled exciter mounted on the generator shaft system.

Excitation power requirement of the generator (with same rating) does not change with change of excitation system. What changes with excitation system is excitation current and excitation voltage requirement. Power practically remain same.

Reply Score 1 for Good Answer
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); pcchatur (1); Phanibabu (1); RAMConsult (3); SolarEagle (1)