Tripping Due to Overcurrent in Earthing

09/19/2015 8:02 AM

Dear All,

Hope you are doing great. We faced Tripping at our Generator 26 MW due to Overcurrent in Earthing. This happened in this sequence. Firstly Our Grid Tie Circuit Breaker Tripped when Sensitive Earth Fault Relay sensed Overcurrent in Core Balance CT. After 3 seconds, Our Generator Tripped although it shoud be on Home Load/ Auxiliary Load. Generator Relay Panel indicated Heavy Fault and 51 N relay tripped by indicating overcurrent fault. We checked the Grid Tie Circuit breaker control panel and reset it. It was closed to continue running the auxiliary of Plant. After that we thoroughly inspected the NGR/ Ground CTs Termination Box of 26 MW Generator. Every thing( Terminations ) found normal. Then turbine was set on rolling and after field excitation was put ON. We clamped ON the Gernerator Earthing and found only 0.083 A. After that Generator was synched to Grid and the system is normal upto this date.My question is that if everything is normal why tripping occurred? One speculation was that Welding was going on at the structure of Cooling Tower Line (Coming to Generator for Cooling). Can a welding job result in sensitive earth fault detection?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Tripping Due to Overcurrent in Earthing

09/19/2015 1:50 PM

That sounds plausible, like a lightning strike nearby....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: Tripping Due to Overcurrent in Earthing

09/21/2015 10:25 AM

You did not state the system voltage but something to consider is that often a ground fault will burn clear when the system voltage is medium or high kV.

It would be a good idea to take a good look throughout the system for arcing damage especially in any enclosed switchgear or other areas where animals can access the conductors.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."