GSU tx OLCTC

09/19/2015 9:34 PM

Does GSU TX has an OLTC in the situation where a generator is paralleled with the grid.
How's possible for GSU TX to increase the secondary voltage(HV) while the tap changer is usually located on secondary side (HV)?, is there a possibility where the tap changer is located on primary side(LV)?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: GSU tx OLCTC

09/19/2015 10:45 PM

The OLTC changes the voltage regardless of which side it is installed on. The reason that they are usually installed on the high voltage side is because that is the low current side and the switching mechanism doesn't have to be as robust. And don't forget you can also adjust the output voltage/VARs via the excitation system.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Anonymous Poster #1
#2
In reply to #1

Re: GSU tx OLCTC

09/20/2015 2:52 AM

The voltage signal is feedback from LV Primary to AVR OLTC, if there was a voltage drop on the grid, generator AVR would adjust the field current in order to match with the voltage grid through the feedback from synchronizer, the tx avr sees this condition as voltage drop, it tends to reduce its winding in order to increase the primary winding (LV side of tx), but the primary side of tx voltage is fed from the generator, no matter how many steps were reduced, the voltage on the primary side is fixed by the generator, my assumption this may cause the secondary side voltage to drop (HT side of tx) as primary voltage is fixed by the generator and also due to secondary winding reduction by OLTC, if this were to happen, the HT side (33kv) would no longer syncronized with grid because the amount of voltage reduction on HT side(33kv) is greater than the voltage reduction by the grid/generator. I'm perplexed how is possible for OLTC step up TX to work if the generator is paralleled with the grid?, what I can see now NLTP is the best option.

Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: GSU tx OLCTC

09/20/2015 1:18 PM

You have a classic problem from control theory science; i.e., two controllers trying to control the same control variable, plus a race condition.

When the OLTC AVR is trying to meet its setpoint it affects the voltage that the Generator AVR senses. This causes the Generator AVR to adjust the terminal voltage of the generator, which in turn affects the voltage that the OLTC sees, which in turn affects the voltage that the AVR sees...ad nauseum...until they are at the end of their ranges.

The problem is complicated by the difference in response times of the two controllers. The generator AVR operates at electronic speeds, while the OLTC controller runs at mechanical speeds plus a deliberate time delay between operations.

In these situations I usually set the OLTC to manual and let the generator AVR control the overall voltage, and manually adjust the OLTC if system conditions force the voltage range to be adjusted, but only a system study can determine the proper operating points for your particular conditions.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 3)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4
In reply to #2

Re: GSU tx OLCTC

09/21/2015 3:49 PM

RAMCONSULT gives a good description of what could be happening.

My thought is that typically the generator will have two modes of operation..

1) AVR Voltage control when it needs to synchronise and connect to the Grid, say with the OLTC preset to middle tap.

2) Power factor control when Grid connected, typically unity where the generator just tries to run at a steady MW and nearly constant amps without reacting directly to volts. N.B. often the OLTC does the voltage or VAr/power factor control at Grid voltage, or just keeping the generator working at its rated voltage despite Grid voltage changes [just consider that rated MVA at 95% volts requires 5% overcurrent from the generator while 105% voltage requires rotor overcurrent].

I am not clear if the question is about a theoretical system with AVR and OLTC or an actual plant. The term AVR [Automatic Voltage Regulator] is commonly used for the "excitation" control system with the general understanding that it is not just a fixed "zero regulation" voltage system but can operate with a current feed back which causes a voltage fall with increasing lagging current (droop) or/and a slower loop which behaves like a human operator who adjusts the voltage knob (often the operator sets voltage set-point via an up/down motor drive or electronic register which can be switched to auto control by a raise/lower controller).

If this is a new fault on a proven plant, is it possible that some (Grid breaker?) auxiliary selection to the AVR/Excitation control [or OLTC] is not operating as it should when connection is made to the Grid??

It is possible an AVR "voltage droop" is not working or is set too small. This would not matter or be noticed until connected to Grid. Once Grid connected, however, the AVR could have excessive gain leading to instability.

67model

Reply