MV Cable Extension

10/18/2015 12:31 AM

Sunday Greetings to All !

I need to extend a 6.6kV 3 core cable by 2 meters to enable termination on a VCB panel.

It is too cumbersome to install a straight-through jointing kit and additional cable just for 2 meter extension

Can I extend the individual leads of the 3 core cable by joining 1 core cables with straight thru jointing kits ?

If anyone has tried it, I would be grateful for sharing the experience

__________________
We Are In Current Control !
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#1

Re: MV Cable extension

10/18/2015 1:45 AM

Assuming that it is inside the enclosure I see no problem with this.

If it is outside the enclosure, then you will need to ensure adequate continuation of the outer insulation over the separate joints, and also, if armoured, earthing of the sheath.

Also, if it is an outside joint, remember eddy current considerations where the single core cables enter the enclosure, ie. through a single entry hole or ensure a slot exists between separate holes.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2008
Location: Mumbai, India
Posts: 14
#2
In reply to #1

Re: MV Cable extension

10/18/2015 2:04 AM

Thanks for the prompt response

The proposed joint is outside the breaker panel but within an underfloor cable trench.

If it is difficult to enter the 3 x 1 core cables through a common hole, we shall replace the gland plate with an aluminium plate or bakelite sheet to prevent eddy current heating

__________________
We Are In Current Control !
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5
In reply to #2

Re: MV Cable extension

10/18/2015 8:36 AM

My advice is to go for a straight through joint at a suitable location near cable trench . It will be safer and make proper termination to the breaker.

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#3

Re: MV Cable extension

10/18/2015 2:22 AM

What does your country/ local codes require? Your splices can be as pretty as a flower but if they're outside of the governing code(s) ...... Not knowing what country your working in, you might want to research it a little more before spending time and money doing something that will not pass inspections, or at least that's what I would do to start with.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: MV Cable extension

10/18/2015 7:43 AM

Oh, damn, I cut the cable twice and it is still too short....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Sep 2015
Posts: 482
#6
In reply to #4

Re: MV Cable extension

10/18/2015 11:58 AM

now, do you even have to say that? I mean the guy is already miserable. Cut too short. I'll call it "irreversible".

__________________
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Register to Reply Score 2 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #4

Re: MV Cable extension

10/18/2015 6:35 PM

Yep. Measure once, cut twice.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: MV Cable extension

10/18/2015 1:59 PM

If the cable has to be longer than the maximum delivered length-even it is a new run-you have to use a joint.

However, 2 m before termination it is not so elegant way to joint it. This point is a source of another possible-

additional- fault [theoretically, at least].

__________________
Julius
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Sep 2008
Location: Mumbai, India
Posts: 14
#10
In reply to #7

Re: MV Cable extension

10/18/2015 10:29 PM

Actually the cable is pre-existing. The fault was in the old VCB panel which caught fire and the cable termination inside got damaged as well. After cutting out the damaged portion, the cable is short by 2m for re-termination in the new VCB Panel. The other end of the cable is 200m long and is buried in the ground with no hope of pulling it up.

Hence we are looking for an out-of-the-box solution.

I have seen HT Aerial Bunched Cables with straight thru joints hanging loose in the air. Hence I felt we could extend the leads by a couple of meters. However most of the people I have asked so far are sceptical. So I guess it needs re-thinking

Check out this image on this link : http://www.tehnosistem.co.rs/str6_eng.html

__________________
We Are In Current Control !
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#11
In reply to #10

Re: MV Cable extension

10/18/2015 11:55 PM

It seems to me that your own link answers your original question!

Now, whether it meets code in your locality and situation is a totally separate question that must be answered before you proceed.

Finally, make sure that, assuming it does meet code, that the splicing is done by someone fully trained in the use of that particular splicing method for that kind of service. 6.6kV splicing is not for beginners!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#9

Re: MV Cable Extension

10/18/2015 9:31 PM

So much for the guesstimate! Now, how can we justify our cost over-runs?? Or, is that just cutting things too close

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#12

Re: MV Cable Extension

10/21/2015 8:09 PM

My suggestion: install a 30 ft pole in the appropriate place to install a junction box on the pole for the connection you need, travel up the pole, going through the air and attach the new cable to the building at proper height. Connect the new end where appropriate .

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13

Re: MV Cable Extension

10/23/2015 12:38 AM

Employ a cable jointer that knows what he is doing. If I had to do this joint I'm afraid "it would be inconvenient" wouldn't be a valid argument.

A trifurcating joint (look it up) is near a metre long.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Dec 2015
Posts: 11
#14

Re: MV Cable Extension

12/14/2015 6:53 AM

It can be done by using individual straight joint kits but each cable should be carefully bunched and insulated. Also the straight through joint kits voltage rating should be matched with the voltage level.

Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mumbai, India
Posts: 14
#15
In reply to #14

Re: MV Cable Extension

12/20/2015 11:57 AM

Thanks for the confirmation

__________________
We Are In Current Control !
Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); dj95401 (2); dkwarner (1); johnmarsh11 (1); JRaef (1); Legolaz (1); Munster (1); spades (1); sunilji (3); TonyS (1); Tornado (1); V.I.Abraham (1)

Previous in Forum: What Happens if Rating of i/c Breaker is Equal to all Individual o/g Breakers   Next in Forum: Insulation Resistance Test for Alternator

Advertisement