Anonymous Poster #1

Grounding System for Power Substation

10/26/2015 3:53 PM

From electrical safety point of view, do we have to interconnect all the transformers' neutral grounding system with other electrical equipment grounding system in a power substation having 400/132/11/.4KV System? and why?

Many thanks for answer

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: Groundong System for Power Substation

10/26/2015 4:35 PM

What do the blueprints specify?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Groundong System for Power Substation

10/26/2015 5:33 PM

Do you have a clue?

I thought not.

If it's homework, look in your textbook.

If it's a question on a job application, leave the room, now.

If you are working on a HV substation, please give the forum the address of the job site.

Eleven practical tips for grounding substations. | content ...

Reply Score 1 for Good Answer
Anonymous Poster #2
#3

Re: Grounding System for Power Substation

10/27/2015 12:26 PM

If <...we...> have to ask in a global Engineering forum, <...we...> as an organisation are not qualified sufficiently to work locally in this area!

  • What does the "for construction" design drawing say?
  • What is wrong with asking the individuals whose names are on the drawing instead of coming here?
  • Is there no-one in the facility that one could ask face to face? It would be astonishing if there were not!
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Grounding System for Power Substation

10/28/2015 10:22 AM

In my opinion, all neutral-transformers and generators- has to be connected to the same power station grounding grid directly or through a current limiting impedance.As it is noted in IEEE 665/1995 :

Eight methods of grounding are identified by IEEE Std C37.101-1993:

  1. High Resistance Grounded (Distribution-Transformer Grounded)
  2. High Resistance Grounded (Neutral-Resistor Grounded)
  3. Low Resistance Grounded (Neutral-Resistor Grounded)
  4. Low Inductance Grounded (Neutral-Reactor Grounded)
  5. Resonant Grounded (Ground Fault Neutralizer Grounded)
  6. High Resistance Grounding-Transformer Grounded
  7. Medium Resistance Grounding-Transformer Grounded

8.Ungrounded

__________________
Julius
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Grounding System for Power Substation

10/30/2015 9:52 AM

I wouldn't want to walk about a substation that wasn't an equipotential zone.

With everyone having to do the fireman's shuffle it would take time to get about the place.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: Grounding System for Power Substation

11/09/2015 11:08 PM

Normally transformer neutral has to have two independent neutral earth pits.So obviously it should not be connected to earth of other equipments.Body earth of transformer can be connected to other earth pits.The local rules on this should alos be considered.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Anonymous Poster (1); lyn (1); nesubra (1); Original_Macgyver (1); TonyS (1)