IGBT power source is of 300 KW used for crankshaft hardening, we found co axial cable faulty and changed the cable, the new cable contained strands of same cross sectional area as the old one.the coaxial cable is used for power transfer from IGBT power source to work head ( matching transformer)
I have the problem of Over voltage or sometimes over current. Can any one tell me if the Co axial cable has any thing to do with these alarms. Insulation resistance between inner and outer layer is OK, also strands are well intact and have not burnt or opened up.
Pl advice,
Good Answers: 804
Re: IGBT Power Source Trips and Shows Alarm of High Frequency and Over Current
11/01/2015 10:19 PM
Did you ensure that the shield integrity is continuous? If not, you can get capacitive Charging current spikes that look like an over current to whatever is monitoring it.
Location: crankshaft producing hub in belgaum,karnataka,india
11/01/2015 11:10 PM
Thank you for the reply . The shield integrity is continuous, this is a water cooled co axial cable, at the jinction where the inner core strands are soldered, and in between outer core there exists a teflon bush of 1.0mm wall thickness and a gap of 2mm exists between OD of inner core and bore of outer core bush, in between this gap is the teflon bush, the strands used are 2sq,mm x 18 nos ( 37 strands of 0.25 mm dia ) teflon coated ,just as original ,
these are not tightly packed inside the tube carrying DM water , thus during movement chances of central conductors moving inside the external conductors may arise. does this change the cable characteristics?
Good Answers: 27
11/03/2015 7:02 AM
"Movement of central conductor" inside the external conductors, may create an unwanted changes in its characteristic impedance! Any movement changes the separation space separating the two conductors. This physical changes in space or gaps may introduce a corresponding net changes in the cable impedance as a result of its varying capacitance between the internal and external electrodes....
vsar
Good Answers: 445
11/01/2015 10:55 PM
Just because two pieces of coaxial cable have the same physical look and feel, does not guarantee that they have the same electrical characteristics.
When you're pushing 300KW of RF energy through a feedline you better be damn sure that it is an exact match for the coax that it is replacing, same exact characteristic impedance, power handling capability, shield wire density/pattern, center conductor pitch, even the length and any bends must be identical.
Then you have to calibrate it and measure its SWR (Standing Wave Ratio) to ensure that it is delivering the maximum power possible to the load.
11/02/2015 12:35 AM
No, it's not with your transmission wire probably but,
  • double check cable connections (sometimes loose load side connection and grounded cause over current)
  • Over voltage is usually caused by bad supply feed or quality (data log if you have the tool 24 hours Voltage supply of IGBT)
  • Over current is cause by low voltage feed on supply of IGBT, for most and also grounded load side lines
Generally, please diagnose first the power supply quality, next is the IGBT circuitry this is how you should approach your problem step by step.
It is best that you require your company to purchase Power supply diagnostics device just like Fluke 1740 if you want a professional and reliable business, or find some cheap alternative if budget does not fit your pocket.
The doctor said "just one post or reply aday in CR4, take it or leave it". I said, "what does that mean?"
Reply Off Topic (Score 3)
11/02/2015 9:54 AM
Dear Sir,
thank you for the reply, Please elaborate over high frequency alarm, what would be the
possible causes. does poor insulation strength of base plate where transformer's secondary is connected through adaptors on a single base plate , give rise to such high frequency alarm in which case secondary of transformer is getting partially shorted?
11/02/2015 10:07 AM
I have no confident about that and I would no further advice you what to do.
If you are in-charge on this, in the first place, you should be will equipped with the technology and science behind it.
If it's not probably a supply quality problem, the issue may involve above (series or parallel RLC circuitry analogy)
I advice you hire or consult an expert on this issue.
Reply Score 2 for Off Topic
11/03/2015 7:24 AM
Added bonus: Pls. study guidelines of Allen Bradley for wiring and Grounding
Good Answers: 122
11/02/2015 10:01 AM
COAX cable is available in different impedance values and are specific to the application.
In sensitive applications the overall length of the COAX cable can affect the controls.
If the issues were not present before you changed the COAX cable it may be that you have installed the wrong cable and/or the new cable or connector(s) are bad.
The length and outside diameter of the center core COAX conductor are critical.
If the center conductor is too small or does penetrate the connector far enough intermittent signal issues will occur and can cause control issues as you have described.
Also; If the machine was in operation when the COAX was damaged it could well be that internal damage has occurred to the IGBT control(s).
I suggest an in-depth examination of the COAX cable first including finite measurement of the center conductor outside diameter with a micrometer and verification that the length meets factory requirements.
I would also suggest you obtain the factory specifications on the COAX cable then buy or rent a cable tester to test the new cable(s) for compliance.
If the cable passes examination then an in-depth control analysis is in order.
United States - Member - New Member Hobbies - HAM Radio - AC9JZ extra
11/02/2015 10:09 AM
You first mentioned
Power Source Trips and Shows Alarm of High Frequency and Over Current.
Then you mention over voltage, and or high current. Please clarify these alarms, and if they are all secondary, or if any are primary. While your focus is on the new cable, what damage was done to the old cable? Was it shorted, or open? Even if the IGBT's seem good, there could be some damage to them, or the circuitry associated with them. Check Gate Drive circuitry, look for any burned resistors or damaged parts. RAMConsult gave you good advise regarding the cable. Have you asked the Manufacturer about the cable, and or problems experienced?
The only dumb question is the one you didn't ask.
11/02/2015 10:18 AM
I suspect the cables are the secondary consequent effect. If problem still persist on their replacement, probably the monster(root defect) is still out there, looking for sometime to attack the new cable and other circuit elements.