FloBoss 600 Calculations , How to Access With Only Front Panel

11/18/2015 9:48 AM

Please we have Vijeo Citect V5.5 getting data from floboss 600 flowcomputer through Modbus TCP, I have accessed one tag in Citect variables file and I need to know if there is any way to know this tag coming from where in floboss 600?? the problem we do not have configuration software for floboss 600 , only we have the CPU of the flow computer with its front panel and no screen and no configuration software.. how to access the data that sent from it to Citect HMI through Mod bus??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: FloBoss 600 Calculations , How to Access With Only Front Panel

11/18/2015 1:49 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#2

Re: FloBoss 600 Calculations , How to Access With Only Front Panel

11/18/2015 3:52 PM

The nature of Modbus is that the master (Citect) queries the slave (FloBoss) and requests data from a specific address/register. The slave responds with the data from that address/register.

Find the Modbus setup in Citect and look for what the address/register is that is being queried.

Most Modbus slaves use a fixed map, meaning that the factory says which data is at which address register. The documentation has a published map/table of which data is located where in which address/register.

Some wireless gateways, PLCs and PACs and one flow meter I've run into have customizable slave maps - the programmer defines which data goes into which address/register. I don't know whether the Floboss has a fixed or customized slave map/table.

Register to Reply