Model : HG32/20-3 + k 601-2 Type Horizontal split
Inlet pr (Min./ Normal/Max.) : 100/101/111 Kg/cm2 abs.
Inlet Temp. (Min./ Normal/Max.) : 480/480/510 Deg C
Extraction pr. (Min./ Normal/Max.) : 27/28/30Kg/cm2
Extraction Temp. ( Normal/Max.) : 336/350 Deg C
Extraction flow in T/Hr. (Min./ Normal/Max.) :20/37/42 T/Hr.
Speed (Normal/rated/): 9095/9510 RPM
This Turbine was retrofitted in 2012 with Electronic Governing System, Since then Turbine and compressor running continuously .
recently Turbine tripped 03 times :
1. indication was ESV open limit switch off. assuming the malfunction of Governor trip solenoid valve, the solenoid valve was replaced.
2. During 2nd tripping , turbine tripped and the indication was same..the indication was ESV Open limit switch off( the Trip Oil Pr. camedown from 9.0 kg/cm2 to 0.0 kg/cm2 in 10 sec) & speed came down from 8970 rpm to 0 in 60 sec.
3. During 3rdtripping - Turbine tripped on DCS, First out logic has logged trip due to Governor. Governor was having trip reason due to loss of speed.
In sequence of Event(SOE) of PLC, first event was ESV Limit switch close & then trip oil pr. coming less than 4.5 kg/cm2 & then 2.0 kg/cm2 & then gov. trip signal.
Request to go through the above problem and suggest remedial actions please.