Dear Experts,
I've started to study about fault currents in transformers and motors. On searching the internet, I came across many documents referring to symmetrical components. Unfortunately I could not co-relate it to my questions listed below, as it involves complex mathematics. How do I understand it intuitively? I mean what is the starting point I can relate to?
My questions are,
1. How does the fault current reflects in the primary side (in the transmission line, not in the windings) of the transformer if a fault (L-G, L-L, L-L-G fault) occurs in the secondary side of a transformer?
2.How much change will the secondary side current and voltage values, if a fault (L-G, L-L, L-L-G, Open circuit in one phase)occurs in the primary side of a transformer?
3.What will be the current and voltage to other phases if a fault (L-G, L-L, L-L-G) occurs in the motor feeder?
4.What will be the current and voltage to other phases if open circuit fault occurs in one phase of the motor feeder?
Thanks beforehand
Re: Understanding Symmetrical Components
01/07/2016 4:57 AM
01/07/2016 6:22 AM
A1) Until such moment as the circuit protective device(s) operate(s), the primary current will be such multiple of the secondary current as is determined by the turns ratio of the transformer subject the core not being magnetically saturated. The current in the primary transmission line is the same as the current in the windings as the former is supplying the latter.
A2) As A1.
A3) It depends upon the nature of the fault. Generally, in a correctly-designed system, the circuit protective device(s) operate(s) before any significant damage is done.
A4) There will be a short-term increase as the motor stalls, then the circuit protective device(s) will operate, disconnecting the motor; from this point the current on the particular motor circuit falls to zero.
Good Answers: 445
01/08/2016 12:17 AM
It would be interesting to know what you mean by "...complex mathematics..." since the word "complex" has multiple meanings in power engineering. Unfortunately Symmetrical Components is both complex and requires complex math, so learning vector math will assist in your understanding of the topic.
Fortunately the specific questions that you asked are standard situations that are covered in most good power engineering texts and handbooks, where they are derived and presented in (mostly) algebraic fashion. One thing to be wary of are blogs, they are often rife with misinformation (CR4 included), get a well respected textbook (Blackburn or Stevenson) that is at your current educational level. The topic is over a hundred years old, and used to be solved on a slide-rule, so you can learn it too.
01/08/2016 1:37 AM
Excellent